Discuss wiring centre in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Status
Not open for further replies.

BLOD

Plumbers Arms member
Plumber
Gas Engineer
Messages
1,308
Has anyone got a wiring diagram for a Tower (Grasslin?) wirerite 24 way wiring centre ?
 
It is one of those boxes that sparks use. Has connectors inside like the ones in a ceiling rose. You probably do get a wiring diagram of some kind but knowing the way sparks wire heating there will be a pile of 3 cores and twin and earths wired whatever way was easiest.

You will have to figure it out by tracing the wires.
 
it's y-plan.
I'd replace it, but they've boxed it in and I can only just reach the terminals with the mm probes
 
And what is the problem BLOD?

rads heat up when only hw is called for & rads never get that hot on ch only - (so looking at the 3w valve plus a few other things) usually start with checking for power on the right wires but the wire from the valve has been extended using flex with different colours into the wiring ctr hence need for a diagram.
 
It is one of those boxes that sparks use. Has connectors inside like the ones in a ceiling rose. You probably do get a wiring diagram of some kind but knowing the way sparks wire heating there will be a pile of 3 cores and twin and earths wired whatever way was easiest.

You will have to figure it out by tracing the wires.

yep that describes it well !
 
3 way valves are usually spring return to h/w only, so I'd be first thinking dodgy valve! Is it spring return do you know?

Rads not getting hot could also indicate dodgy diverter or restricted flow yeh?

On ho****er only that's all you'd expect to get yeh?
 
3 way valves are usually spring return to h/w only, so I'd be first thinking dodgy valve! Is it spring return do you know?
Usually, but if the hw goes off before the heating does the motor will hold it open to the heating side. (until the hw switches back on)

Rads not getting hot could also indicate dodgy diverter or restricted flow yeh?
Yes.

On ho****er only that's all you'd expect to get yeh?
Yes. Feel the outlet pipes from the valve and see where the heat is passing through.

Sorry Diamond. Thought it was Blod asking that one. I need new specs.
 
Last edited by a moderator:
already had the head off the valve and get an even temperature to hw & ch no matter which way the spindle is turned, so I guess the rubber ball is shot.
Probably get away with just changing the valve (honeywell) but would like to check power is getting to the right places.

thanks for the help tamz & diamomdgas
 
Get one of those plug and sockets big gas use.

Thanks Tamz - good advice.
I put one of these in, so could check power to & from the valve etc, ended up changing the body (ball was loose, seperated from the stick).
 
Status
Not open for further replies.

Reply to wiring centre in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock