Hi,

I will try to explain best I can, please bare in mind I am currently in a learning stage so just trying to understand the process behind things.

A building with three floors and 69 rooms. How do you work out the pressure needed on the hot water system? I’m sure there is a calculation to work out the flow rate and pressure. Sometimes the top floor experience low pressure on the hot water, I believe it is currently supplied at 2.5 bar.

I would like to try and do the calculations to work out the correct pressure setting.

appreciate any help or advice given.

Thank you.
 
There’s a difference between pressure and flow rate, and there’s a calculation used for working out which each floor needs by a way of working out what is needed to be fed on those floors. More experienced engineers than me might say an accumulator could be used?
 
Chances are the booster system isn’t designed for total load or is starting to fail eg pump seals etc
 
There’s a difference between pressure and flow rate, and there’s a calculation used for working out which each floor needs by a way of working out what is needed to be fed on those floors. More experienced engineers than me might say an accumulator could

Thank you for the reply. Do you know the formula for the calculation please? I would quite like to work out the pressure per floor. A hot water expansion vessel is used on the system which is set at 2.5 bar unsure if this is correct or how to work out the correct pressure.
 
Thank you for the reply. Do you know the formula for the calculation please? I would quite like to work out the pressure per floor. A hot water expansion vessel is used on the system which is set at 2.5 bar unsure if this is correct or how to work out the correct pressure.

2.5 bar cold so let’s say 3 bar per flat and 20lpm how many floors ?
 

So let’s take 2.6m to allow for dropped ceilings etc that gives you 10.4m need to pump so adds 1.04 bar ontop of your outlet pressure requirement so 4.04 bar required to give you 3 bar 4 floors up

Working on the 70% rule that’s 50 flats needing water at the same time so that’s 1000lpm eg 20lpm for each flat

So 4.1 bar and 1000lpm is your duty cycle
 

Reply to Water pressure for block of flats in the Commercial and Industrial Plumbing Forum area at PlumbersForums.net

Similar plumbing topics

Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
319
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock