Hi all.
Pulling hair out (not much left)
Compact 25HE - Ignition sequence ok when demand for DHW, burner lights and water is hot at the outlet.
However, the temperature continues to rise until the primary thermistor puts the fire out. Pump continues to run and the appliance re-lights once cooled (the time of this varies).
Same thing happens during heating demand.
I have unplugged primary thermistor and plugged in a new one leaving it external to the heat exchanger. The boiler runs continuously under this test, kept an eye on temperature and shut tap before tripping high limit stat.
Plate to plate, heat exchanger, thermistors, pump, diverter valve and motor all checked - clear. Venturi's cleaned, flue not blocked. Fan ok.
Am I missing something simple? Advised landlord he may have to call vokera.
Any pointers appreciated in advance.