Kewat66

Gas Engineer
Messages
119
Hi All,

looking at a vaillant ecotec plus 824. It is coming up with f75. This seems to relate to low pressure and pressure sensor. Have changed the pressure sensor, checked the pump, change the divertor valve ( that was original fault). System pressure is 1.5 and still no joy. Hot water fine. Starts the sequence but fails when it gets to fan and pump running (s05) then fault code F75 appears. Checked the manual and vaillant web site and they say could be a number of related issues!
i am now think PCB board but any ideas before this is bought.

thanks
kewat66
 
Could be too much inhibitor in the system. It froths up in the pump and does not allow the sensor to read the pressure drop when the pump kicks in.
 
There's a thermal fuse on the top of the boiler. If you follow the wire down to the plug hanging on the RHS link it out. If it lights then the thermal fuse has popped. You cannot get them from vaillant...it's a new heat exchanger (not such a good boiler now are they??). Had a lot of to - ing and fro - ing when with BG regarding vaillant. Vaillant say it cannot guarantee safety (alarm bells call 'elf n safety)if this pops. it's a con.
 
if the thermal link has popped its a different fault code my bet is on crud behind the sensor drain it remove sensor then start to fill see if it clear youll need a towel
i can never understand why vailants dont have a screw in the well to allow you to drain the water that collects there when changing parts
 
It can only be the pressure sensor, buy a spare and plug it in dry. Fire the boiler by pushing it in manually. If it runs ok it's some sort of blockage not pump.
 
I have removed the pump head and cleaned, removed the new pressure sensor, removed the sensor housing and cleaned the filter. I tried all the suggestions so far and kept getting the same issue so as a last resort put back the old diverter valve and no fault just the original fault of diverter valve not giving any dhw so I am now assuming the new diverter valve has an issue on it. It seems to be a new modified part with a different electrical connection so of to the shop in the morning to exchange. Fingers crossed!
 
I have removed the pump head and cleaned, removed the new pressure sensor, removed the sensor housing and cleaned the filter. I tried all the suggestions so far and kept getting the same issue so as a last resort put back the old diverter valve and no fault just the original fault of diverter valve not giving any dhw so I am now assuming the new diverter valve has an issue on it. It seems to be a new modified part with a different electrical connection so of to the shop in the morning to exchange. Fingers crossed!

You've spent some time in front of that boiler mate?
 
Is that not the vailants with the stupid black hose that clogs going into heat exchanger, I've changed a few of them on the 837 models,
 
If you've had the pump head off... was there a whiteish residue? If so open a drain off and the filling loop and flush some fresh water through. A trick from a friend who is a Vaillant engineer.
 
I've had this one before, spent ages working it out.
The pump had slowed down, I know you said you checked this but was the pump strong.
i weak pump can give this fault.
 
How do you check for a weak pump on these? When you take the centre screw out, it pee,s out a jet of water. Usually in the direction of the pcb!
 
Status
Not open for further replies.

Reply to Vailant ecotec plus 824 f75 in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock