hi all
called out ole lady hot water problem
ravenheat csi 85 condensing GC 47 581- 20
the central heating side fine
hw side , went through the mi,s test, according to Mi,s alls well. tried unsuccesfuly to get technical. flow good pressure good diverter good , i yr old plate h/exchanger boiler fired modulated to temp ran for 5 mins cut out truth, never worked on ravenheat so be gentle lol
 
the sensor pans out ok it cuts out it doesnt come back in red flashing light and has to be reset manualy
apreceiate the replys lads
 
Could still have problem with plate EX if system is very dirty, or scale if in hard water area.
 
hi jt yea hard water area is a understatement i had a look in her kettle ooohh yea scale thanks jt diamond an dave
 
it will not have scaled up in a year id go for dirty hex whip it out and give it a good cleanplenty of shaking and run under a tap see what you get out
 
Marlow / High Wycome will scale up quick, used to live near there !
 
ok guys im on it today ill clean the h ex out ill let you no the outcome
 