Just a quick one really - I've noticed a couple of the boilers I've been servicing have the pipe from the PRV running in 15mm copper for a short run and then they exit into a 32mm plastic waste pipe. I've also seen this on a new installation as well.
I thought that it had to be in copper all the way - or am I wrong?
 
Needs to be pushfit waste pipe and trapped

Also need a tundish on the prv pipe out the boiler
 
So does that mean that solvent weld waste pipe has a lower tolerance, and if so how would anyone know which pipe has been used once it's installed?

Yes correct and you need to stub it above so you can tell
 