Hi all new to this site

I'm planning on a New CH system with Combi-Boiler will all new Rads also this house currently has a warm air system which is being replaced.

1. I would like to run the pipes in Hep2o barrier i believe. idea is to drill holes into joists and feed 22mm pipes I have a long landing so will be the main run.

2. i was thinking of channeling in a few pipes on the ground floor walls to conceal the pipes, is this a good idea? what can i put in the channel to prevent any long term issues?

3. is it worth me buying a right angle drill to make holes? as will be making a few holes everywhere

look forward to your thoughts thanks
 
You really do hate platic dont you happy flyer ! I dont understand why ! People mis use it and it fails ! FACT ! If you mis use copper it fails ! People moan about plastic but it works and does a very good job ! May be a different plastic but all ne water mains are plastic ! And there fine. You cant exactly use copper on the collector for GSHP.
 
now you guys have a lot of negative feedback on plastic.
Im confident on routing / running pipes rads etc. would be nice if I could learn on how to solder. I'll have to look if I could a crash course in plumbing soldering or something.
 
You really do hate platic dont you happy flyer ! I dont understand why ! People mis use it and it fails ! FACT ! If you mis use copper it fails ! People moan about plastic but it works and does a very good job ! May be a different plastic but all ne water mains are plastic ! And there fine. You cant exactly use copper on the collector for GSHP.

On31

It's simple, you don't need to be a plumber to fit plastic, you don't need to a plumber to fit copper but it does help and you are right GSHP is a plastic derivative which in the main lends itself to plastic, I don't like to see it being used when you have a choice, BTW I am not on my own about only using copper there are others, copper does look nice when it's installed right, plastic is best hidden under the floor of behind a cupboard door it can never be made to look good, or am I wrong and the jobs I have seen have been plumbers from hell and it really can be made to look good, post some photos of work you have done in plastic, BTW anyone one else who has some bespoke plastic works, I will not be holding my breath.

Tony
 
You really do hate platic dont you happy flyer ! I dont understand why ! People mis use it and it fails ! FACT ! If you mis use copper it fails ! People moan about plastic but it works and does a very good job ! May be a different plastic but all ne water mains are plastic ! And there fine. You cant exactly use copper on the collector for GSHP.
Let's not forget plastic gas mains :) and even oil :)
 
plastic is fine, in the right hands.

most plumbers who dont like it have had bad experiences with it because it was poorly installed originally. Ive plumbed 4-500 plus new build houses in the stuff and had no major issues, houses ranging from 1 bed flats to 6-7 bed large houses. Only really seen problems on bad workmanship on other jobs tbh.

modern building methods and joists tend to make plastic the prefered choice in new construction, its here to stay. You either need to embrace the tech or reduce the percentage of work you can tender/quote for.
 
I don't know how many others have said this but it's also my view:

Plastic is okay as long as it's out of view and fitted correctly.

Don't think there's much more to say it about really.
 
Wellill have a loon for some work ! Seen a few boiler rooms in plastic except for where copper needs to be used ! I just think you have a personal mission to ban plastic ! Yes people fudge up using plastic but they also make the same mess in copper and compression fittings ! I dont see the problem ! I know a plasterer that to be honest is a decent plumber would happily let him install a CWS or somthing other hand i know a plumber who is also gas safe that i wouldnt let solder up his own gas run or change a tap un supervised ! Its the world we live in that these parts are avalible and people do DIY. But it cant be blamed soley on plastic ! Not having a go.


Btw has is plastic gas mains mean rpugh plumbers ? All new gas mains are plastic ! Look right across the uk gas network !
 
Think I know where I was going wrong I think I wasn't cleaning rubbing the new copper joints. Just seen this YouTube video given me some confidence [video=youtube;WpHQ0WCDlFI]http://www.youtube.com/watch?v=WpHQ0WCDlFI[/video]
 
My original plan was to plumb 2 possibly 3 of the bedrooms from underneath with making holes and feeding plastic pipes through. You guys have now put me off. Now can I run copper pipes from underneath as a lot of the ceiling is going be be removed on the grd floor.
 
Id run it in plastic any day over copper 100% cleaner faster easier and no one has even thought about mentioning about flux corrosion if using copper and solder joints?? need to flush because of crap in the pipe ????? i think that 1 point for me there:yes:
When we was diy sos big build we used plastic for 99% of the plumping had NO probs had a British gas guy come and help out run a New gas line (copper) and guess what had a leak
 
Id run it in plastic any day over copper 100% cleaner faster easier and no one has even thought about mentioning about flux corrosion if using copper and solder joints?? need to flush because of crap in the pipe ????? i think that 1 point for me there:yes:
When we was diy sos big build we used plastic for 99% of the plumping had NO probs had a British gas guy come and help out run a New gas line (copper) and guess what had a leak

How long have you been plumbing Supper?
 
on and off about 2 years we do alot of bathrooms and kitchen soo it helps to know the basics rather then sub it out do it your self im looking into getting into college.
if i can to learn more and get more of a insight into plumbing and gas I like plasic because its clean fast and if done right it looks good well i like it
only trade we sub is gas and sparks

we try and renew all plumbing the room as its better for us to work on new pipe work and rout it how we want it and where we want it
 
Last edited by a moderator:
ahh ok plastics have risks.
more risk of rodents chewing through to get to the water.
if not cliped properly then under the expansion and movement as they heat up and cool down they can rub a hole over a period of time.
I personally dont trust the joints so i only use it from point a to point b over a long run. just two connections at either end.

Regarding the gas leak.
Gases have a far smaller structure than liquids meaning that a leak would show up with air or gas but not with liquids.

Do you pressure test your pipework? you will quickly find this.

Plastics do have their place in modern pumbing however i would not use it on heating unless i have too.
Flushing the system isnt the worst thing in the world it's just part of heating installs in my view.

in the past 3 years ive been to more leaks on plastics than copper.
and with the copper its either 15+ years old or poorly fitted in the first place.
Plastics have generally been very well fitted but has leaked regardless.

as you gain more experiance you will find it similler to this.

Good luck !
 
Id run it in plastic any day over copper 100% cleaner faster easier and no one has even thought about mentioning about flux corrosion if using copper and solder joints?? need to flush because of crap in the pipe ????? i think that 1 point for me there:yes:
When we was diy sos big build we used plastic for 99% of the plumping had NO probs had a British gas guy come and help out run a New gas line (copper) and guess what had a leak

Flux is not a problem if a decent flux is used. Personally I prefer grease based fluxes - not really very corrosive at all & you still have to flush a heating system anyhow & clean excess flux on outside pipes soon after soldering. Copper is by far the best for standard heating systems.
I have 3 samples of plastic pipe that plumbers have installed & they burst. One of them was non barrier pipe on a mains pipe in a kitchen that froze & burst. The other two are barrier pipe that ballooned, split etc, when on different heating systems that had both overheated. But it is the plastic fittings with hot heating water in them that is a worry. And, remember this - if a soldered fitting is done right, it is for life, but a plastic push fit, if they push off, which they do & for various reasons, will mean full bore, full flow major flooding. If I was to ever accept plastic pipe/ fittings, it would be in a basement where no damage could occur. And I haven't mentioned rodents!
 
Last edited:
ahh ok plastics have risks.
more risk of rodents chewing through to get to the water.
if not cliped properly then under the expansion and movement as they heat up and cool down they can rub a hole over a period of time.
I personally dont trust the joints so i only use it from point a to point b over a long run. just two connections at either end.

Regarding the gas leak.
Gases have a far smaller structure than liquids meaning that a leak would show up with air or gas but not with liquids.

Do you pressure test your pipework? you will quickly find this.

Plastics do have their place in modern plumbing however i would not use it on heating unless i have too.
Flushing the system isnt the worst thing in the world it's just part of heating installs in my view.

in the past 3 years ive been to more leaks on plastics than copper.
and with the copper its either 15+ years old or poorly fitted in the first place.
Plastics have generally been very well fitted but has leaked regardless.

as you gain more experiance you will find it similler to this.

Good luck !

1King55,

I agree with everything you say here, you just missed one thing, it looks a bugger when you lift the floor board or open the door, it is impossible to make look good, if you all don't mind this is my main beef. If you were brought up as a fully trained plumber in the 60's as I was then you will know appearance was number one, it had to be water tight, plumb, straight, bend following each other, falling or rising the right way,clipped neatly, plastic can never fit that bill and never will. As you say it has its place, it has on an only one advantage I would consider is a good point, when you break into it you don't need to worry about water dripping down the pipe, with copper end feed it's a pain. I think plastic will always fail were it has not been fitted correctly and you cannot blame it for that, time alone will tell 1king55 I don't have much of that left to hang about and find out, I will leave it to you lads, but IMO plastic has not help you in anyway in fact I think it will damage your ability to call yourself plumber in the sense that I was when I was young only a plumber could do plumbing that has now change forever, I could teach my 11 year old granddaughter how to put an outside tap on in an hour does that mean she got a trade.

I have now asked you all when was plastic first used for domestic central heating and no one has come up with an answer maybe you all think that the 15 mm and 10 mm plastic you now see Guest etc is the first well you be wrong it's been on the market before and die a death, I used it in the late 60's, when Yorkshire first brought out there mini bore manifold, they were painted in bright blue and they made to 4 port brass mini manifold, a company call SYR also brought over from Sweden GEECOL a steel pipe 6 mm and 10 mm in Europe they didn't lift floor board to installed heating the routed two groove in the floor and laid the pipe in the groove and then tacked is piece of sheet metal off a roll to cover it about 2" wide, they designed there system on a very high temp drop F/R as high as 50 C they sealed all their systems and ran their boilers up to 100 C so you had 100 C flow and about 50 C they used SYR radiators convectors coils on the back with hardly any water in them , the whole 8 rad system had no more than a few gallons of water in them. Turn the boiler on and you were up to temperature in mins, I fitted a few but the convectors were very noisy ticking like a clock, they crimped the coils on the back of the convectors instead of tack welding, they system die a death, and so to the then plastic Impalyene, so you see you plastic chaps its all been done before, most of you were born, but not all of you.

Cheers 1King55
 
I fully agree with this.

when i look under a sink and see it i wince.
Ive only used it on my bosses jobs for runs in screed.
connection at either end gong straight to copper as we avoid any connections in the floor.

If its less than 3 metres i just bend the copper to suit then protect it.

I admit that quite alot of the art has been lost.
 
who gives a t oss what it looks like when under floor boards as long as it works I'd go with plastic with drilled joists everytime, happyflyer since when has a gshp been a derivative of plastic your talking nonsense!
 
1King55,

I agree with everything you say here, you just missed one thing, it looks a bugger when you lift the floor board or open the door, it is impossible to make look good, if you all don't mind this is my main beef. If you were brought up as a fully trained plumber in the 60's as I was then you will know appearance was number one, it had to be water tight, plumb, straight, bend following each other, falling or rising the right way,clipped neatly, plastic can never fit that bill and never will. As you say it has its place, it has on an only one advantage I would consider is a good point, when you break into it you don't need to worry about water dripping down the pipe, with copper end feed it's a pain. I think plastic will always fail were it has not been fitted correctly and you cannot blame it for that, time alone will tell 1king55 I don't have much of that left to hang about and find out, I will leave it to you lads, but IMO plastic has not help you in anyway in fact I think it will damage your ability to call yourself plumber in the sense that I was when I was young only a plumber could do plumbing that has now change forever, I could teach my 11 year old granddaughter how to put an outside tap on in an hour does that mean she got a trade.

I have now asked you all when was plastic first used for domestic central heating and no one has come up with an answer maybe you all think that the 15 mm and 10 mm plastic you now see Guest etc is the first well you be wrong it's been on the market before and die a death, I used it in the late 60's, when Yorkshire first brought out there mini bore manifold, they were painted in bright blue and they made to 4 port brass mini manifold, a company call SYR also brought over from Sweden GEECOL a steel pipe 6 mm and 10 mm in Europe they didn't lift floor board to installed heating the routed two groove in the floor and laid the pipe in the groove and then tacked is piece of sheet metal off a roll to cover it about 2" wide, they designed there system on a very high temp drop F/R as high as 50 C they sealed all their systems and ran their boilers up to 100 C so you had 100 C flow and about 50 C they used SYR radiators convectors coils on the back with hardly any water in them , the whole 8 rad system had no more than a few gallons of water in them. Turn the boiler on and you were up to temperature in mins, I fitted a few but the convectors were very noisy ticking like a clock, they crimped the coils on the back of the convectors instead of tack welding, they system die a death, and so to the then plastic Impalyene, so you see you plastic chaps its all been done before, most of you were born, but not all of you.

Cheers 1King55
I did ! Clearly you were to busy listening to your own voice to notice :)
 
ive done hundreds of houses in plastic, its fine but it should not be on show imo. you should always use copper for fixtures, tails etc...... Its stronger, it does not move under pressure changes and its adaptable for all situations. nothing worse than looking under a kitchen sink or bath and seeing plasitc flopping about.

you want a min 600mm copper tail at each fixture (except hidden drops to rads), 3m of copper off your boiler F AND R connections.
 
Last edited:
ive done hundreds of houses in plastic, its fine but it should not be on show imo. you should always use copper for fixtures, tails etc...... Its stronger, it does not move under pressure changes and its adaptable for all situations. nothing worse than looking under a kitchen sink or bath and seeing plasitc flopping about.

you want a min 600mm copper tail at each fixture (except hidden drops to rads), 3m of copper off your boiler connections.

Thats a more realistic use!

still i like my copper :D
 
I am saying no more about it for fear of contraception, you fit what you want where you want, on top of or underneath where you want, I know what looks good and I don't need to go the Spec-savers....:1eye:
 
Buy all the tools you can get. Tools are good but only if they cost £4-500 a whack. They give you a buzz buying them.
Then straight through everything with your new tools because they can.
Direct is best and cheaper:lol:
 
Status
Not open for further replies.

Reply to planning route for new CH system and advice on Hep2o pipes in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

P
Replies
7
Views
989
Ermintrude
E
D
Replies
4
Views
2K
davevincent
D
L
Replies
7
Views
3K
TBServices
T
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock