Have a 2 bedroom semi detached house which is 35 years old. One of the bedrooms is distinctly colder than the rest of the house.

We got a Worcester greenstar 34 cdi combi fitted 2 years ago, with a wireless room thermostat fitted in the living room.

There are 5 radiators in the house and a chrome towel radiator in the bathroom. The 5 radiators are all original,with no TRVs fitted,just a screw (on/off) valve on each.

Upsatairs and the hallway is generally much colder than the living/diner/kitchen where the room thermostat is currently set to 22 degrees. The coldest room, is 16-17degrees(bedroom) and the other bedroom 20ish degrees.

If i turn the thermostat up to say 26 degrees it increases the temp in the bedrooms so i know the rads aren't blocked on needing bled etc.

I have had extra loft insulation added and i am considering having cavity wall insulation installed too.

I realise i could shift the room thermostat into the hallway (where it is colder) to increase the temp in the bedrooms,but that would make the living room too warm?

I basically want to know how i can balance the temperature throughout the house better (especially upstairs)
 
probably a good idea to move the stat into the hall, and yes the living room would then get to hot, this is where TRV's come in, you need them fitting in every room apart from the bathroom. This is where I call it, fine - tuning comes in where you then adjust the temp in each individual room rather than the whole house.
 
probably a good idea to move the stat into the hall, and yes the living room would then get to hot, this is where TRV's come in, you need them fitting in every room apart from the bathroom. This is where I call it, fine - tuning comes in where you then adjust the temp in each individual room rather than the whole house.

So if i renewed all 5 radiators amd fitted a TRV on every one,would i need a lockshield on every rad too?
 
here are the rad sizes

600x1000
600x1600
600x700
600x900
600x900

What kind of price inc TRVs,fitting etc should i be looking at to get them renewed by a plumber?

The rads have 2 pipes at one end, not one pipe at either end,so i realise i need copper pipe to run to each end.
 
Could also be that the radiators are under-sized for that room, or a problem with pipe runs & size , But need to have better controls fitted, will save you money on your gas bills
 
probably a good idea to move the stat into the hall, and yes the living room would then get to hot, this is where TRV's come in, you need them fitting in every room apart from the bathroom. This is where I call it, fine - tuning comes in where you then adjust the temp in each individual room rather than the whole house.

I've been reading that any room stat should be fitted in the main room and no TRV valve fitted in that room?
 
From what you describe you have a micro-bore system with twin entry valves, size of the boiler you have upgrade rads to double's up grade controls / TRV's -Room stat Not going to be a cheep thing to upgrade rads now quite expensive, get a least 3 quotes.
 
You should of had trvs fitted when the boiler was installed 2 years ago.
 
So if i renewed all 5 radiators amd fitted a TRV on every one,would i need a lockshield on every rad too?
A lockshield valve is most definitely needed when you have TRVs. They are used to balance the system, i.e make sure each rad has the correct flow.
 
We have twin entry rad valves fitted as pictured below.

Getting some conflicting info on what set up to go for, namely where the room stat should be situated and whether or not the rad in that room should have a TRV???
 
Last edited by a moderator:
probably a good idea to move the stat into the hall, and yes the living room would then get to hot, this is where TRV's come in, you need them fitting in every room apart from the bathroom. This is where I call it, fine - tuning comes in where you then adjust the temp in each individual room rather than the whole house.

My bathroom has a TRV fitted.......is it not actually necessary?:confused5:

Just curious as to why the bathroom should be any different to other rooms.....is it because most people like the bathroom warmer than the rest of the house or something like that?

Cheers.
 
Get rid of these old radiators , pipe work if solid floor one pipe will need to run on skirting, if wood floor then can be altered under floor, looks like 8mm pipe going to valve
 
Get rid of these old radiators , pipe work if solid floor one pipe will need to run on skirting, if wood floor then can be altered under floor, looks like 8mm pipe going to valve

Thanks for the reply.

Yes i realise the pipe will have to run along the skirting.

If i leave the room stat in the living room,should i not fit a TRV in that room?
 
Status
Not open for further replies.

Reply to One room colder than others in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock