Handed me a kicking today!!! :censored:
Thermocouple wouldn't stay lit tested it 16 mv at the tip, interrupter tested ok, changed the gas valve and still the bloody thing wouldn't stay lit! After fiddling with the hump of junk for 20 mins about to head to the merchants to rant about broken gas valves of the shelf. I noticed the smallest and I mean smallest bit of rust on the connection between the thermocouple and interrupter. Cleaned it with a bit of wire wool and woosh! That satisfying sound when the bugger lights!
Some days I really hate boilers!
Thermocouple wouldn't stay lit tested it 16 mv at the tip, interrupter tested ok, changed the gas valve and still the bloody thing wouldn't stay lit! After fiddling with the hump of junk for 20 mins about to head to the merchants to rant about broken gas valves of the shelf. I noticed the smallest and I mean smallest bit of rust on the connection between the thermocouple and interrupter. Cleaned it with a bit of wire wool and woosh! That satisfying sound when the bugger lights!
Some days I really hate boilers!