Hi all. Hope you can help.

Been to look at an ideal icos he 18 l & f code. Done everything from the flow chart and changed the flame detection probe. Contacted ideal and they're advice was to boil the kettle a few times and flush the heat exchanger to clear the aluminium oxide build up.

Ive also cleared the trap and cleaned out the sump at tue bottom of the heat exchanger. The water i poured in ran out freely with no restrictions.

Im stumped. Could it be a faulty gas valve as it runs fine for 5 or 10 minutes then cuts out. Leave for a minute and reset and it'll come back on.
 
Done
 
You have not broken any rules.

Glad you got the answer you need.

An extra 10000 'experts' out there now able to give advice
on fixing icos's.


You are 100% correct it shouldn’t have been on an open forum , I was more interested the OP was gas safe. As for the 10000 new icos experts they now have an idea how to fix one of the many icos fault codes , half the fault codes dont relate to the specific fault anyway , and I have heard theres only 30 left lol .
 
You have not broken any rules.

Glad you got the answer you need.

An extra 10000 'experts' out there now able to give advice
on fixing icos's.

Give over 10000 new experts guess you've never been on u tube have a look at the icos fixing vids

Doubt there 10k left in the uk
 
Bugger !! Get ready potential nightmare now.
When it cuts out , does it cut out “dead” no fan etc , or do you get the flashing blue light , then goes to fault
 
Bridgend area South Wales .

There's not really alot in there to go wrong really is there. Hope a new valve sorts it.

Ideal helpline happily dishing out info without checking i was gas safe too

Reason I asked is I have a working / secondhand valve , you could have cadged it if you were closer.
Let us know how you get on .
A lot of the wiring on the Icos harness / loom is starting to split and break but to be fair , they are old boilers now .
 
L A is overheat according to MI's

Screenshot_20181215-134002_Drive.jpg
 