Did a boiler swap sat and wired s plan. I bought the honeywell easy wiring centre to make things easy. I cut links 2 and 4 but hw zone valve would open on htg demand had me puzzled for a while. The instructions on the lid of wiring centre were not clear. In small print it says cut link 1 if using programmer. One to watch for
 
The salus centre is not bad larger than standard 10 way and you just link out the terminals with wire links
 
Surprises me in this day and age that something of a proper plug and play nature hasn't come out.
 
Ha ha never come across them before. Considering its Honeywell the pack isn't actually that expensive. Found for £180
 