I have had ongoing problems with my boiler and no heat or hot water for 10 days now. I am a full time carer for my 90 year old disabled Father who is a dementia sufferer so things are getting a little dire and quite smelly too.
HISTORY
Local GS Engineer replaced gas valve and igniter pcb and reset gas pressure and it worked for 2-3 days gradually getting hotter and hotter with kettling and increasingly frequent tripping of the overheat stat
Boiler fires up on both CH and DHW demand.
Burner goes into immediate full pressure burn on CH ?!
After 8-10 seconds boiler starts to kettle and primary heat exchanger (PHE) pipes and pump too hot to touch.
PHE flow is red-hot to the inlet of Diverter valve but heat goes no further.
If DHW demand then boiler bangs violently as cold mains goes through DHW exchanger.
Switch off ... then seconds later overheat stat trips . Heat confined to PHE pipes and pump . No heat evident in CH flow from diverter valve but some heat creeps through diverter valve and the bypass pipe to DHW exchanger .
As far as I can tell the pump is working and the system is at approx 1Bar and air fully vented.
I’m thinking either pump not working , or diverter valve jammed open to DHW exchanger giving short loop or primary heat exchanger blocked or CH flow blocked.?
I’d appreciate your thoughts on this before I strip it down again and fit a new diverter valve and pump and flush the system and boiler yet again!
ps Engineer refuses to attend again saying new boiler required. Well she wants to fit a new boiler I guess
HISTORY
Local GS Engineer replaced gas valve and igniter pcb and reset gas pressure and it worked for 2-3 days gradually getting hotter and hotter with kettling and increasingly frequent tripping of the overheat stat
Boiler fires up on both CH and DHW demand.
Burner goes into immediate full pressure burn on CH ?!
After 8-10 seconds boiler starts to kettle and primary heat exchanger (PHE) pipes and pump too hot to touch.
PHE flow is red-hot to the inlet of Diverter valve but heat goes no further.
If DHW demand then boiler bangs violently as cold mains goes through DHW exchanger.
Switch off ... then seconds later overheat stat trips . Heat confined to PHE pipes and pump . No heat evident in CH flow from diverter valve but some heat creeps through diverter valve and the bypass pipe to DHW exchanger .
As far as I can tell the pump is working and the system is at approx 1Bar and air fully vented.
I’m thinking either pump not working , or diverter valve jammed open to DHW exchanger giving short loop or primary heat exchanger blocked or CH flow blocked.?
I’d appreciate your thoughts on this before I strip it down again and fit a new diverter valve and pump and flush the system and boiler yet again!
ps Engineer refuses to attend again saying new boiler required. Well she wants to fit a new boiler I guess