Thanks for all responses, even the sarcastic one at the start..!! Just trying to get different opinions from a consultants badly specified drawing.[/

Wasn't trying to be sarcastic just thought you might have been a student looking form easy answers - my bad!

My understanding is the discharge point can be at high or low level but offer no danger to anyone.
It can be fed into the soil but only with local authority approval.
If possible has to be visible at tundish and termination point.
Pipework has to be sized to carry full bore release away without backing up
 
Thanks. Aware of all that. Just that I have an install where consult says to go onto existing discharge point but it's not correct. Can't get correct drop and discharge doesn't terminate to safe place, therefore just thinking about what date regs came in as original instal wrong.
 
If its a new install surely it has to comply with current regs ?
 
Thanks for all responses, even the sarcastic one at the start..!! Just trying to get different opinions from a consultants badly specified drawing.[/

Wasn't trying to be sarcastic just thought you might have been a student looking form easy answers - my bad!

My understanding is the discharge point can be at high or low level but offer no danger to anyone.
It can be fed into the soil but only with local authority approval.
If possible has to be visible at tundish and termination point.
Pipework has to be sized to carry full bore release away without backing up

should say "or"
 
Thanks. Aware of all that. Just that I have an install where consult says to go onto existing discharge point but it's not correct. Can't get correct drop and discharge doesn't terminate to safe place, therefore just thinking about what date regs came in as original instal wrong.

doesnt really matter about original install not being right, as long as you know ot to connect onto it as it would then make your install illegal, wish i had £1 for everytime i have heard, "but i just reconnected it the same way it was in, so its not my fault"
 
Totally agree. Just wondered if anybody new exact date regs came in so I can pass back to consultant
 
april 2010
http://www.planningportal.gov.uk/uploads/br/100312_app_doc_G_2010.pdf

it clearly states the accepted ways of terminating a discharge pipe and the requirements needed if into any wastes system.

i think building control is consulted over wastes termination because many waste systemc cant cope with the temps and you may have to prove that the waste you are connecting to is designed for high temps and the only reasonable route.
 
Last edited:
many discharges are terminated over footpaths by front doors which is wrong as if it runs in winter and then freezes then it will cause a danger, so its best to have either a drain or soft ground/gravel below away from slabs.
 
You do also want it away from where its likely to land on people, as someone previously said the water will be hot, so either low down or away from a spot people regularly walk along or stand around.
 
Status
Not open for further replies.

Reply to G3 Building Regs in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock