Hi, I have a bosch heatslave 20/25 oil fired boiler with a slight problem, the central heating works fine but the hot water out of the tap starts off warm but soon runs cold or just cool, could this be the heat exchanger, any body help please. Thank you, Chris.
Firstly Im sorry to hear you have one of those, must have been fitted by a Gas fitter...
Secondly: Try these:
[Engineers very welcome to duplicate with amendments/ additions to below - its late and I might get it wrong....]
Open the top and CAREFULLY feel the temperature of the 4 pipes coming off the plate heat exchanger:
The 2 bigger ones are the primary flow and return - with the boiler running (careful: HOT HOT HOT) and the prog switched to Hot Water - do both pipes feel the same temp? (best method of course is with a thermostatic probe of some sort).
If no, does the hot water control stat (dial) click? when it does, is the circulating pump running?
If yes, then it looks like the heat passing through the store and plate isnt obstructed so all good on that front.
If above is ok, get someone to turn a hot tap on, you should hear a click at the flow switch.
One smaller pipe is the mains coming in cold, the other is hot water out. Does the hot water out feel the same temp as flow and return at first?
I found a few times that the heat exchanger has been scaled up so the heat cant get out of the store and the HW control stat constantly satisfied so the boiler doesnt fire, pump doesnt run so no heat gets exchanged.
There is a way to check this but not for non-engineers ears Im afraid.