Search the forum,

Discuss Baxi 80 HE runs then locks out. in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Status
Not open for further replies.

armyash

Esteemed
Plumber
Gas Engineer
Subscribed
Messages
2,653
I tagged a long on a job today for the above boiler. Engineer i was with thought the problem was just on HW. tap/shower running, temperature fluctuates a lot and boiler can go to lock out. I said to customer does it happen on CH she said she hasn't tested so i put CH on also and after 5 or so minutes it went to lock out. Sounds like there is a lot of air going around the boiler.

Right, parts changed so far: Flow sensor, gas valve, plate heat ex, electrode leads and PCB.

What would you be looking at? AAV or maybe pump?

Thanks
 
Flue seal.

The blue one (originally red i think depending on age) the one off the top of the causation box.
 
Unless we're talking the later mid combi 80 he then perhaps heavy corrosion in the cylindrical secondary circulator top right of the combustion chamber.

I may be getting my models mixed up its been a few months since I've touched one
 
There did appear to be a slight flame lift. Guy I was with has called Transco out saying governor needs looking at as he was not happy with pressures at the gas valve.

It was a fairly old looking boiler.
 
Multi parts visits always require the basics checking first that often get over looked.

Flow rate, gas rate, BP if possible and combustion readings if all are as per MI then start looking at components.

Temperature fluctuations in hw will also require more then one outlet checking as it could be back flow or faulty blending valve or mixer.

Temp fluctuations also need the resistance checking on NTC sensors if you haven't got them ring technical baxi tech are mustard for those.

Also by pass setting (if adjustable) as if the system is poor quality water content the path of least resistance is always the bypass which will prematurely modulate the burner.

Gritty div valves or worn DHW pressure differentials also leave the back door open on heating circuits and by passes. Fire up from stone cold on hw only and keep your hand on ch flow pipe monitor for heat increase.
 
There did appear to be a slight flame lift. Guy I was with has called Transco out saying governor needs looking at as he was not happy with pressures at the gas valve.

It was a fairly old looking boiler.

Was it the square ally heat ex same as the solo he?

Any idea on the working pressure at the meter and again at p1 on appliance gas valve that'll indicate if it's a regulator fault or gas pipe work under sized.

Flame lift also indicates to faulty seal. But again if it's the square type check the burner. The felt ones should all be replaced regardless of condition and the ceramic ones used to split on the metal at the rear as it met the ceramic.
 
Multi parts visits always require the basics checking first that often get over looked.

Flow rate, gas rate, BP if possible and combustion readings if all are as per MI then start looking at components.

Temperature fluctuations in hw will also require more then one outlet checking as it could be back flow or faulty blending valve or mixer.

Temp fluctuations also need the resistance checking on NTC sensors if you haven't got them ring technical baxi tech are mustard for those.

Also by pass setting (if adjustable) as if the system is poor quality water content the path of least resistance is always the bypass which will prematurely modulate the burner.

Gritty div valves or worn DHW pressure differentials also leave the back door open on heating circuits and by passes. Fire up from stone cold on hw only and keep your hand on ch flow pipe monitor for heat increase.

I think we will be going back so plenty of stuff there to check. thanks
 
Equally if you can hear air get it out. Those flow switches can be precious, especially when pipe work goes up and over the boiler
 
This guy a BG engineer you with?
That the old combi instant thing?
Check pump. If guy BG should have limpet which does work quite well to tell if pump ok. Otherwise screwdriver method.
Check thermistors.
Otherwise maybe blockage?
 
Was it the square ally heat ex same as the solo he?

Any idea on the working pressure at the meter and again at p1 on appliance gas valve that'll indicate if it's a regulator fault or gas pipe work under sized.

Flame lift also indicates to faulty seal. But again if it's the square type check the burner. The felt ones should all be replaced regardless of condition and the ceramic ones used to split on the metal at the rear as it met the ceramic.

To be honest I didn't look too closely. It was his job and being new I didn't want to step on any toes. Just trying to find possible solutions so if i go back again with someone i can make a few suggestions.
 
To be honest I didn't look too closely. It was his job and being new I didn't want to step on any toes. Just trying to find possible solutions so if i go back again with someone i can make a few suggestions.

Never be afraid to speak up. We are all guilty of over looking the simplest of stuff.
 
This guy a BG engineer you with?
That the old combi instant thing?
Check pump. If guy BG should have limpet which does work quite well to tell if pump ok. Otherwise screwdriver method.
Check thermistors.
Otherwise maybe blockage?

I used to love that! Like a little lie detector that was.
 
80 HE IS A BARCELONA WITH COMBI GUTS,not worth repairing IMHO,utter junk,if it was a baxi 80 e or 80 he eco then yes,worth sorting
 
I remember the Barcelona had those awful float switches that were forever getting bogged down with magnetite.

Oh crap I'm getting palpitations thinking about the Phex replacement
 
I remember the Barcelona had those awful float switches that were forever getting bogged down with magnetite.

Oh crap I'm getting palpitations thinking about the Phex replacement

phex is a right pig on those
 
Status
Not open for further replies.

Reply to Baxi 80 HE runs then locks out. in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
323
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock