If I am looking at your boilers M.Is then 4.3 - "a variable duty pump should be set to give a temp diff of no greater than 20deg C"
"Important F&R pipe sizes - up to 18kw = 22mm, >18kw =28mm"
The flow rate required to provide 18kw @ 20 degC would main that your pump would loose approx 1M head just pushing that amount of water through the heat exchanger if you needed it full 30kw you would loose over 2.5Metres.

Your existing pump is a 5M head but that is the max it can push with no or little flow. Moving approx 0.215L/S it would only develop a pressure of approx 3.7M head, less the boiler 1M, would leave approx 2.4 M for the rest of the system. Not likely to be enough to overcome the resistance you have put in by re-piping in 10mm.
 
Fit a Grundfos pump with proportional pressure function? God knows, that's why I'm asking! Someone else must have come across this before?
Yes Chris thats why they were invented.
If you fit one would you need a by-pass ??
I don't think you do & have had my one at home closed for couple of years now with an Alpha 2 installed.
But if you do want to provide the minimum flow then why not use close coupled tees instead of LLH (to expensive) to provide hydraulic seperation. You are going to buy a new pump anyway so give it a go!!
 
Thanks, makes sense to me. Although is 3.5m head sufficient for the longest microbore to manifold circuit of 18m? My rough calculations would suggest not.
It's not just the length of the pipe which is important. You have to take into account the flow rate, which depends on the size of radiator and the temperature differential. For example:

Resistance of 18m of 10mm pipe connected to a 2kW rad with a 20C differential is approx 0.58m, with a 10C differential it is approx 1.94m. The flow rate has doubled so the resistance increases by four times.

Upload your rough calculations and I can take a look at them.
 
It's not just the length of the pipe which is important. You have to take into account the flow rate, which depends on the size of radiator and the temperature differential. For example:

Resistance of 18m of 10mm pipe connected to a 2kW rad with a 20C differential is approx 0.58m, with a 10C differential it is approx 1.94m. The flow rate has doubled so the resistance increases by four times.

Upload your rough calculations and I can take a look at them.
It's not just the length of the pipe which is important. You have to take into account the flow rate, which depends on the size of radiator and the temperature differential. For example:

Resistance of 18m of 10mm pipe connected to a 2kW rad with a 20C differential is approx 0.58m, with a 10C differential it is approx 1.94m. The flow rate has doubled so the resistance increases by four times.

Upload your rough calculations and I can take a look at them.

I won't embarrass myself as they are obviously wrong and too basic. It's plastic pipe too which might make a difference?
 