I have a job where I need to run 30 metres of 28 mm and 10 metres of 22mm copper tube. Now there is no gas hob in the place so I need to light the gas while purging. What right do you guys make up in this scenario. Cheers
Discuss Purging long gas supply in the Plumbing Jobs | The Job-board area at PlumbersForums.net
according to this app on a g4 meter with 35m of 22mm no fittings comes to 0.0305m3Just done it manually and I make it 0.03014m3
with a wooosh!30 x 0.00053 = 0.0162 + 10 x 0.00032 = 0.0194 (IVp) + 10% (IVf) = 0.02134 + 0.008 (IVm) = 0.02934 x 1.5 = 0.04401
If the pipe is feeding a boiler just turn it on. It will purge itself to a source of ignition.
according to this app on a g4 meter with 35m of 22mm no fittings comes to 0.0305m3
30 x 0.00053 = 0.0162 + 10 x 0.00032 = 0.0194 (IVp) + 10% (IVf) = 0.02134 + 0.008 (IVm) = 0.02934 x 1.5 = 0.04401
Just done it manually and I make it 0.03014m3
30 x 0.00054 = 0.0162
10 x 0.00032 = 0.0032
meter = 0.008
total = 0.0274
10% = 0.00274
Total = 0.03014
Don't think I've missed anything?
Every app you use will prob give different answer.
If you want accuracy you need go old school and work out using your fingers and toes with standardised formula.
I got 0.02934 volume for a G4 meter.
Technically if its a g4/U6 and pipework 28mm or under you don't need to bother working out the IV. The PV is 5 x cyclic volume (0.002) = 0.01
You've added 10% to the pipework before adding meter volume, right?
that size is the iv of your result/size over 35m of 22mmWhere are you getting 35m of 22mm? I thought we were looking at 30m x 28mm + 10m of 22mm??