B

buckley plumb

been to a main eco today about 3 years old. heating is fine but on hw boiler would not modulate seemed to heat water and turn burner on and off - fitted hw thermistor as hw thermistor fault come up occsionaly. this seemed to help and when the hot tap was turned on full the boiler would modulate - turn tap to half flow burner would hunt up and down trying to modulate down after 2 min it would modulate to low and be ok .I am thinking now heating thermistor as this controls the primary flow
 
Do a resistance check on it, it'll be in the book. Also put it in to chimney sweep, and see if it runs ok on low. Had a faulty gas valve on one of these.
 
Do a resistance check on it, it'll be in the book. Also put it in to chimney sweep, and see if it runs ok on low. Had a faulty gas valve on one of these.

resistance was ok mate but didn't check at different temps .run ok on low rate on htg
 
was thinking that but made no attempt to modulate at first . and after 2 mins ran ok until tap turned off and on again to do same cycle
 
Id chuck another ntc on it, parhaps try running it out of its pocket so it can't sense and see if it still modulates.
 
will order one tomorrow the one on main heat ex is £40.

Ouch, for an ntc? If it's a dry pocket, remove from pocket .Plug it in so it can't sense temps and see what happens.
 
Last edited:
I just plug a ntc loose to test see if it makes any difference to the way it fires. before changing wet pocket. but sounds like hex?
 
Status
Not open for further replies.

Reply to main eco in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock