Discuss Vaillant boiler change in operation in the Central Heating Forum area at PlumbersForums.net

Not sure if relevant and/or whether it might point to the room stat as issue, but boiler fires up and stays on until temp reached for hot water.
That Honeywell stat has a number of versions/options (I think there's a letter at the end of the serial number indicating which), and one version has a "heat anticipator" the exact operation of which I don't understand. It might be the little resistor (heater) found in some thermostats to reduce the hysteresis of the sensor. Could that be contributing to the issue - it shouldn't I guess?

IMG_0412.jpeg
 
Yes, that's how the anticipator works, if the stat is knocking off the boiler then the pump will run for the d.1 the overrun set time if it's going into anticycle then the anticycle time is set in d.2 there is also a s parameter telling you if its overrun or anticycle. The remaining anticycle time will also be displayed in one of the d parameters I think, if boiler is in recycle, remaining anticycle time is shown in d.67.
d.1 overrun defaults to 5 minutes, the anticycle actual time is per table, below, if thehe target temp is 75C then the annticycle time is 1 min irrespective of the set time which has a default setting of 20, apart from setting 1 (min) which strangley enough gives a actual anticycle time of 2 minutes.

1702929755194.png
 
Last edited:
Thanks for all replies. I thought I was out of warranty, but on checking, I have till March. Called Vaillant engineer out, who fitted new pcb and flow and return sensors which appears to have fixed early recycling issue.
 

Reply to Vaillant boiler change in operation in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

Hi My oil boiler keeps locking out after running for 30/40 minutes! I then try to reset it but it won’t fire back up! I have to leave it for...
Replies
19
Views
853
I recently had a new 2023 Vaillant ecoTec plus 630 (30kW) system boiler installed along with a Low Loss Header (LLH) in my house. I have 21 rads...
Replies
10
Views
802
Hi all Wondering if you could help with this strange issue. I have a Vaillant ecotec 637 (set to 20kw part load) which was connected via a LLH...
Replies
57
Views
3K
I currently have a Vaillant ecoTEC Plus 438 system boiler which is 13 years old. I have been having problems with the boiler which potentially...
Replies
6
Views
708
A
Hi, I have Worcester combi boiler which has developed a 'fault' recently. When I switch the heating on, the fire in boiler starts for a second or...
Replies
0
Views
340
Andy Jackson
A

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock