Discuss Vaillant boiler change in operation in the Central Heating Forum area at PlumbersForums.net

Messages
45
My Vaillant boiler now only fires up for around 30 secs then goes off. The egg timer symbol then appears and flashes for several minutes. After that it fires up again and heats the rads. Would be grateful if anyone could suggest why this is happening. Thanks.
 
The boiler is cycling. Ie. Cutting in and out too frequently. The egg timer is in effect blocking the boiler from firing, until the anticycling time limit has passed.
 
Is this happening at its first startup say in the morning or is it after a zone shuts or TRVs start closing in with boiler on for some time?
Its probably exceeding its target temperature by 5C and going into recycle, what is the target temperature set to?.
What model Vaillant?.
 
Is this happening at its first startup say in the morning or is it after a zone shuts or TRVs start closing in with boiler on for some time?
Its probably exceeding its target temperature by 5C and going into recycle, what is the target temperature set to?.
What model Vaillant?.
Happens every time the boiler fires up, when room temp drops below desired temperature. Flow temp set at 75 degs. Only happens the once, and then boiler operates normally after a few minutes until desired temp reached. Boiler is Vaillant ecoTEC plus 418.
 
Have you got a manual or/and a automatic (ABV) bypass valve, if a ABV check its setting index, the system temperature may still be too high after the last shut down to allow it not to reach 80C and burner trip on the initial fire up, if you have a 3 port valve then bypass not required.
Can you see what (d.01) the pump overrun time is and (d.02) the anticycle time likewise.
Can you also check the flow/return (d.40/d.41) temps next time its firing and also the circ pump make/model/mode&setting.

Your name rang a bell there so I looked back through your thread on the last? problem with this boiler, you said the engineer changed a sensor then, do you know what sensor he changed?.
 
Last edited:
Happens every time the boiler fires up, when room temp drops below desired temperature. Flow temp set at 75 degs. Only happens the once, and then boiler operates normally after a few minutes until desired temp reached. Boiler is Vaillant ecoTEC plus 418.
Bit more info. If I bring boiler on by turning room stat up, boiler comes on until it reaches 75 degs. If I wait until room temp falls below room stat setting, boiler comes on only for 30 secs by which time it has only reached around 35 degs and then goes off and egg timer symbol flashes for a few minutes before boiler comes on again until it reaches 75 degs.
 

Reply to Vaillant boiler change in operation in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

Hi My oil boiler keeps locking out after running for 30/40 minutes! I then try to reset it but it won’t fire back up! I have to leave it for...
Replies
19
Views
853
I recently had a new 2023 Vaillant ecoTec plus 630 (30kW) system boiler installed along with a Low Loss Header (LLH) in my house. I have 21 rads...
Replies
10
Views
802
Hi all Wondering if you could help with this strange issue. I have a Vaillant ecotec 637 (set to 20kw part load) which was connected via a LLH...
Replies
57
Views
3K
I currently have a Vaillant ecoTEC Plus 438 system boiler which is 13 years old. I have been having problems with the boiler which potentially...
Replies
6
Views
708
A
Hi, I have Worcester combi boiler which has developed a 'fault' recently. When I switch the heating on, the fire in boiler starts for a second or...
Replies
0
Views
340
Andy Jackson
A

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock