anybody help i have a vokera compact 24 red light keeps coming on i have changed both thermistors and pressure is at 1 bar i reset it and it runs for abit then goes to red again any help i am gas safe registered
 
check sensing & spark electrode is it still sparking when burner is lit ?????
 
Last edited by a moderator:
no stops sparking when lit boiler runs fine then when it gets warm red light comes and boiler wont work till you reset it
 
gas man its funny you should say that when i changed both thermisters i had my dinner on job and it run fine on and off for 1/2 hour so i put casin on went to my next job 15 mins later got call boiler red light on again do you think it could be high limit stat thats failing
 