Hi,

I have two indirect water cylinders (Gledhill) connected to a gas boiler (Vaillant). The system is setup/programmed so that the tanks heat up twice a day for about 2 hours. When the tanks start to heat, one of them makes a loud vibrating noise, sometimes for about 15-20 mins, sometimes for longer. The noise seems to be coming from the hot water return pipe (i.e. the pipe taking the hot water back to the boiler). If I hold that pipe (it has insulating foam) tightly close to the cylinder then the noise stops.

This has been happening since we moved into the property about 9 months ago. I was worried that it's getting louder, but my wife thinks it's the same as it always was.

I was wondering if anyone can tell me ...
  • What is the likely cause?
  • How much do I need to worry? We're booked for a service in a couple of months anyway so could just get our plumber to look at it then, but do we need to get him out sooner?
Many thanks,
Antony
 
There have been numerous posts about these, have a look at this......

and

 
Too much flow through the return needs a lockshield gate valve fitting on the return from each cylinder 100% will fix the problem

Leave them fully open turn the boiler on to heat one up at a time and slowly close the lockshield gate valve until the vibration stops should be around 4-5 full turns etc
 

Reply to Vibrating hot water return pipe from indirect cylinder in the Central Heating Forum area at PlumbersForums.net

Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock