Currently reading:
secondary return copper or speed fit

Discuss secondary return copper or speed fit in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Status
Not open for further replies.

jonnyswamp

Plumbers Arms member
Plumber
Gas Engineer
Messages
1,824
I think I know the answer but I'll ask all the same, has any of the manu's brought out something for sec rets recently?
Just about to start a farm house with 4 bath/shower rooms and cyls in the middle of building on top floor with all outlets fairly close (within 8 m) Now they want the cyls in leanto building (boiler house) off the one pine end, so now need a sec ret, was going to use plastic for first fix as there is a load of full width 10 x 12 oak beams with 25mm above and below them for pipe runs etc
Its going to be an absolute tw@ to run copper, I'm OK price wise as its a client (architect) alteration, just could do with not being there any longer than I originally allowed (other jobs etc)
So.......copper or plastic
 
think you'll find you cant use plastic on 2ndry returns, been the rule since plastic came in use, manufacturers ruling not regs.
 
I was hoping they may have came up with something by now, seeing how they want us to use their shyte
Copper it is then
 
Is it not recommended for the full length of the hot water system or just from the last draw off back to the cyl?
 
None of it. Copper copper copper. If your struggling for secondary return route. Not best practice but if short use 10mm microwhore
 
How about pex or tectite flexible metal system?
Just had a quick read through "qualpex" spec sheet and it states that it can be installed on hot water systems that are continuously used at the following parameters,
12bar @ 20c, 4 bar @ 82c, 3 bar @ 92c and short term up to 114c, but I couldn't find anything specific to secondary returns maybe worth a phone call for future ref

edit all done today in copper now
 
Last edited:
Hep2o can be used on secondary returns where the temperature does not exceed 65°

• Hep2O® should not be installed
in ringmain installations.
A ringmain is a water-replenished
circulating system maintained at a
constant high temperature to
provide a permanent source of hot
water to its distributing pipes.
Typical locations where ringmain
systems are used are hospitals or
hotels which distribute constant hot
water to wards or rooms at a
distance from heat source.
This restriction does not apply to
domestic systems operating
intermittently at temperatures less
than 65°C where a design life of 50
years as detailed in BS 7291: 2001

copied from Hep2o Technical manual
 
But erv 6 bar so could be 86c at 6 bar - tprv blows at 10 bar or 90c. Pipework isn't allowed to be weaker than safety valves. Ask plastic telecoms to explain that one
 
and I presume a one off fault condition is not the problem, it's the constant high temp's that it's not tested against?
 
No pipework should be designed to withstand 1.5 times highest fault pressure. Begs the question why u can use plastic on dhw..... Because when it's hot it's got an open end - drawing water off.
 
86° wouldn't go through through the return if your controls turn it of at a lower temp the fault temp would be in the tank not the return pipework
 
Controls are assumed not to work in a worst case


Where is this information please?

You'd have to be pretty unlucky to have every single control fail, boiler stat, overheat stat, high limit stat. I think the least of your worries would be whether or not you used hep.

If if this were the case then we'd have to assume the t&p relief failed as well, so we'd better only install unvented cylinders in blast chambers.
 
Status
Not open for further replies.

Reply to secondary return copper or speed fit in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock