Hi, guys Multiglow fire type Genesis instruction: burner pressure 18.7mbar, net heat input 6.3Kw. just one test point between valve and burner. I checked burner pressure was 20mbar and I adjusted, now is 18.7mbar ok but I checked gas rate and is 4.4kw burner blocked? operating pressure on meter is 23mbar is it ok? can I put this score on landlord forms, section operating pressure instead of heat input?
 
as you dont have any gsr credentials you wont get an answer yet I'm sorry to say, push some more plumbing posts first
 
If you are gsr please increase your post count to 10+ then send a PM (Private Message) with your gsr details to either Gas man - http://www.ukplumbersforums.co.uk/users/8668/ or Redsaw - http://www.ukplumbersforums.co.uk/users/2718/ who will check you and then give you access to the gsr private forum.