Did gas cert on this yesterday. 2,8m horizontal flue. It gas rated ok and flame was good. Put analyser in and off the scale
So put in air test point and products of combustion picked up. Found boiler flue elbow seal pushed right into elbow not sealing fitted it as it should be and got aps fault. Opened front to let air in to start boiler and fitted back quick. All readings fine. Just aps fault. Replaced aps but still the same do these suffer weak fans.
So put in air test point and products of combustion picked up. Found boiler flue elbow seal pushed right into elbow not sealing fitted it as it should be and got aps fault. Opened front to let air in to start boiler and fitted back quick. All readings fine. Just aps fault. Replaced aps but still the same do these suffer weak fans.