OK, can you post a close up photo of the Drayton data label, we will then see, once and for all, what way the 3 ports are positioned.

You said the "TheGrundfos pump arrow on the front is pointing anticlockwise so is pumping up." can you post a photo of this, the arrow is normally on the side of the pump body and points either straight up or straight down. Sometimes, rarely, there may not be a arrow but if you look at the black asterisk I have placed in both photos below, you can determine from the ridge/bulb on the pump body which direction its pumping in as the start of the ridge will be closer to the pump inlet.

Can discuss the excessive air later depending on findings, above.
 

Attachments

  • Pump pumping upwards.jpg
    Pump pumping upwards.jpg
    271.7 KB · Views: 15
  • Pump pumping downwards.jpg
    Pump pumping downwards.jpg
    271.6 KB · Views: 21
Last edited:
Apologies for butting in - I am interested! The Drayton/Invensys valve seems not to be a mid-position type.
Does the symbol on the side suggest: in 1, out on 2 or 3? (or that's what the plumber thought!?)
Most suppliers are saying it's "obsolete" (apart from the above) and I can't find a data sheet or spec 🤔
IMG_0500.jpeg
The actuator below is just 2 position:
And yes, too much time on my hands on a weekend morning! 🤪
 
Last edited:
It mustn't be, as the the normal type is like a T with the pump pumping into the T "bottom" and the CH & HW on top of the T, however, its worked for years apparently but the left hand pipe to the CH has the cold feed teed into it, if it is like the traditional 3 port then the pump is pumping into the CH port A, if CH only selected or both CH&HW then it will work but if HW (port B) only selected then port A will be closed and the pump will be running against a closed valve with no flow to the HW coil or something like that which would surely have been noticed.
 
Apologies for butting in - I am interested! The Drayton/Invensys valve seems not to be a mid-position type.
Does the symbol on the side suggest: in 1, out on 2 or 3? (or that's what the plumber thought!?)
Most suppliers are saying it's "obsolete" (apart from the above) and I can't find a data sheet or spec 🤔
View attachment 87531
The actuator below is just 2 position:
And yes, too much time on my hands on a weekend morning! 🤪
Just noticed that 2 position now, you can get a 3 port diverter valve (2 position) or a 3 port (mid position) valve.
 
Just noticed that 2 position now, you can get a 3 port diverter valve (2 position) or a 3 port (mid position) valve.
I'm familiar with 3-port mid position etc etc. Basically I was coming to the conclusion that this early commercial Drayton is a 2 position diverter, supported by the symbol on the side, the fact that the actuator seems to be 2 position, and thus concluding that the basic plumbing (ie the pump position) might be correct for this particular valve?
And I tried to offer some evidence to support the theory, given that the OP hadn't provided pics that could fully identify the valve and actuator.
 
Last edited: