Vaillant Eco tec plus 2 (new ecotec)
F70
Check coding resister (on harness right hand side of main heat x)
Check gas type plug on pcb
Check all cable plugs for poor connections.
Check plugs with any faults. female connections spread open causing poor contacts.
 
Glow worm cxi no display or lights board check.




If there is no display, there are some other things ratherthan the boards which can take the display out.

Any of the low voltage components can also do that, so wealways say to disconnect the 3 connections on the left hand side, J1 J4 and J2and see if the display comes back, if it doesn't then you need to ease J13 offthe top centre so you can see the metal tracks underneath, and see what voltageyou are getting on the first track on the right hand side. It should be reading15-16 volts DC, this is the feed to the display board by the main board so ifyou are not getting that then it is the main board, if you are then it is thedisplay board.
Most of the time we do recommend in changing them bothtogether as some of the new software doesn't always like the old software, soeven if if you do or don't get the voltages it still might need both boardsreplacing.


 
Vaillant 824e Turbomax Plus comes up with fault code F28. Did all my resistance and voltage check and still nothing happening. It goes all the way to ignition but does not fire. Hence decided will go next day with a new gas valve, turned up next day without one just wanted to check what could be wrong, when I took it out it had water in it. Don't know how it got in there. But after drying it out everything working perfectly fine. Saved few bobs for the customer and earned few more for myself.
 
Last edited:
I went to a ferrolli optimax he locked out on f37 low pressure there was presure in it and no blockage to the low pressure switch changed the low pressure switch still the same spoke to ferrolli it's no low pressure it's caused by a power surge to the board to get it to reset " press reset for 10 sec wait for ts,press reset and let go immediately it will show p1, press bottom + once p2 will display, press top - to go back to p1, 00 will appear( it needs to be 01) use top + &- to change then press the bottom + once to back to p2, then press top + and 01 should be displayed then press and hold reset for 10 sec and it should be reset! Hopefully will save someone 40 quid for a Low pressure switch
 
en-fault-finding-guide-tmg-mmi-sz20r1205-page-001.jpgAlways handy to have..
 
before you start any fault finding check the three esentials
pressure
is there water in the boiler dont trust the guage whack half a bar in ive had many gauges reading 1bar when theres realy nothing in it
power
is there power to the boiler
gas
is there definatley gas at the boiler once spent 20 mins to find a fault and the the gas valve under the boiler was in the off position always best to crack a union or put a guage on
 
before you start any fault finding check the three esentials
pressure
is there water in the boiler dont trust the guage whack half a bar in ive had many gauges reading 1bar when theres realy nothing in it
power
is there power to the boiler
gas
is there definatley gas at the boiler once spent 20 mins to find a fault and the the gas valve under the boiler was in the off position always best to crack a union or put a guage on

Had same on a duo tec , ages checking then thought would check outlet at meter ... 3mb
 
If you get a leak from the tube where flow turbine is on Greenstar, usually the adaptor behind the turbine has disintegrated.

If you can't get the temp to ramp to max on a Flexicom, then before getting multimeter out etc, take out and clean condense thoroughly. Trap, flush through HEX and check pipe is clear. Had this twice passed on from other company's unable to fix with thermistors. :thinking:

Intermittent ignition on a Solo/Promax. If it's on the new style all in one PCB then when it's lit, tap the PCB housing near yellow sticker. Can get it to drop out if PCB is at fault.

Glowworm CI, if you are getting PCB error as fault code (F13??) then check APS is not stuck on before fan has run, as it throws up PCB error.
 
If you goto a intergas combi compact constantly going to 11 fault code, before checking sensors and harness.....remove and clean flow switch as debris can get on the paddle and make it stick in hot water mode.
 
if you have just removed on a service the burner and fan from a duotec HEA/gold/titanium/heatmax/promax combi and you get e133 error make sure you have fitted the silicone tube back to the manifold venturi and not the spare port
 
If you goto an ecotec pro/plus that is starting up when switched on and display fades and the boiler conks out....check to see if pressure switch is the pink one and replace this first as it could be drawing all the power away from the rest of the boiler....had one yesterday.
 
For gledhill pulsacoil 3 also check that the little float switch in header tank hasn't been broken off/that it makes a connection to send power to the board, no power will go to immersions if it is not making a connection.
 
Last edited:
Biasi M96(24/28)SM/C2
Round black APS
boiler fires up for a few seconds then goes off, continues to spark. After a few attempts the lock out led comes on. Works when the combustion chamber is off.

check flue was fitted correctly as the white seal bends when pushing the elbow into the flue and doesn't sit right.
Fault only starts after the warrenty period is over :(
Remove the complete flue clean and pour water in the top of the boiler to clean out the heat exchanger. Done 3 of these in the past year.
 
Biasi M96(24/28)SM/C2
Round black APS
boiler fires up for a few seconds then goes off, continues to spark. After a few attempts the lock out led comes on. Works when the combustion chamber is off.

check flue was fitted correctly as the white seal bends when pushing the elbow into the flue and doesn't sit right.
Fault only starts after the warrenty period is over :(
Remove the complete flue clean and pour water in the top of the boiler to clean out the heat exchanger. Done 3 of these in the past year.

Got one of these that displays aps fault mostly in ch mode. New aps fitted already, I'm going too go back and check flue and Venturi. Any other ideas?
 
Worcester Greenstar 28i Jr

If your customer is getting below/above average heat on the DHW hold fire on the PHE for a second & get out your thermometer & multimeter.

Check the resistance on the DHW NTC, for example I had a GS 28i JR that was not getting past 40C @ the DHW outlet the Kohms reading was out by 0.5

10C - 19.9 Kohms
20C - 12.3 Kohms
30C - 7.9 Kohms
40C - 5.2 Kohms
50C - 3.5 Kohms
60C - 2.4 Kohms
70C - 1.7 Kohms
 
And check the diverter head hasn't been hanging off for three years since install(by someone else) and sending heat around rads everytime hot tap turned on. I was checking thermistors when valve head droped off.
 
Here's 1 for commercial oil burners. I'd say Croppie's seen this. Have seen this happen a couple of times on Riello RL burners.
If the plant room door is open on a sunny day, sun shining in can make d burner go to lock out.
Photocell can pick up light shinning down boiler sight glass, say when boilers up to temperature, photocell picks up some light, the panel thinks there's a flame like a big lump of carbon on d head burning, and locks panel out.
You'll go out on call, Murphy's law it'll be a dull day and there'll b no apparent fault.
 
Here's 1 for commercial oil burners. I'd say Croppie's seen this. Have seen this happen a couple of times on Riello RL burners.
If the plant room door is open on a sunny day, sun shining in can make d burner go to lock out.
Photocell can pick up light shinning down boiler sight glass, say when boilers up to temperature, photocell picks up some light, the panel thinks there's a flame like a big lump of carbon on d head burning, and locks panel out.
You'll go out on call, Murphy's law it'll be a dull day and there'll b no apparent fault.

Don't it throw you! Bit of insulating tape, job done.
 
Vaillant ecoTecs

If you have random unrelated intermittent faults.
Get a cuppa turn it on heating and watch the display. If the boiler flow temperature jumps around from say 55 to 62 and back in the blink of an eye the PCB needs replacing. It can take 5-10 min to start doing this.

Video on next post.
 
Last edited:
Vaillant EcoTec Plus - if you fit an external expansion vessel make sure it goes on the return! Had a nightmare with one today, kept getting F75 (no pressure increase when pump spins). Eventually found out it was because I'd fitted the expansion vessel on the return - NEVER AGAIN!!
 
Glowworm hxi model - when they turn off after being constantly in use they may show f5.
Overheat stat needs to be reset normally looks red and is located near the top left
 
Turned off and drained down an arriston microgenus to find on re filling and powering on the fan wouldn't spin.
Checked voltage to fan = nada, assumed PCB. Was about to go buy PCB before remembering the main circuit flow switch needs to make before your get fan/ignition.
Air in diaphragm - bleed pump = save your self a fortune and embarrassment.
 
Another one iv had a few of recently is a blocked condensate rubber tube on the greenstars (cubed trap not the bottle) - give it a squeeze and work it out. And of course wash it through with some water
 
Ariston Microgenus He fault code e34, MI's say APS not making. If the boiler fires up when you take the inner case off then you need to remove the restrictor ring in the flue. Spoke to a Ariston engineer on a product training day who told me to undo the flue elbow and remove the restrictor ring as it's not supposed to be there and it actually worked.
 
Biasi M96(24/28)SM/C2
Round black APS
boiler fires up for a few seconds then goes off, continues to spark. After a few attempts the lock out led comes on. Works when the combustion chamber is off.

check flue was fitted correctly as the white seal bends when pushing the elbow into the flue and doesn't sit right.
Fault only starts after the warrenty period is over :(
Remove the complete flue clean and pour water in the top of the boiler to clean out the heat exchanger. Done 3 of these in the past year.

cOLD OR lIKE WARM ?
cHEERS BUDDY
 
Greenstar Jnr etc with cylinder HEX.

Firing then shutting down going to lock out, crazy CO readings and wouldn't react to gas valve being set up, rubber hose from gas valve had perished and split. Blocked condensate also common if these haven't been serviced, you can usually hear this though, had one recently where the grit that gathers in WB's had totally choked the limestones in the soakaway causing an air lock. Took a bit of sussing out as the condensate wasn't backing up....
 
Remeha advanta plus
When using hot water pretty much straight away even before pre purge the boiler locks out with a e13 fault, hex thermal fuse fault.
If you reset and run heating all will be ok as soon as hw demand e13 fault. I linked out thermal fuse during hw demend and still e13 fault.i checked thermal fuse for continuity all ok, its a known but unusual pcb fault. In my case i removed hw flow sensor so would not activate hw mode and it ran happily for the heating until i returned with pcb 30mins swithed and set up.
 
Ideal logic combi sump. Don't waste your time taking the heat ex out. Rip the old sump off, then use a 42min push pit 90degree elbow on the plate heat ex working it from left to right. Will clip the sump into place.
 
Had a Vaillant ecotec pro 28 yesterday - F75. Checked sensor, was ok but changed anyway, renewed pump head, still no pressure rise detected and still F75. Ended up being a PCB fault o_O

Can be electronic side of sensor, had a few (including new ones) where sensor reads decent pressure, but gauge inside boiler reads zero :eek:
 
Attended a 24ri a few days ago with just the blue light flashing - would not fire & was working up until yesterday.
Worcester fault sheet suggested:
Gas pressure
Co2 levels
Electrodes
Gas coils
Possibly pcb.
In other words could be anything.
I picked up a set of electrodes & a gasket.
On removal the rectification electrode was a bit short but the electrodes were sparking.
Removed the fan & found part of the rubber flap in the air-gas mixing chamber was missing. The other bit had passed through the fan & was sitting in the bottom of the burner.
Another merchant visit new flap installed & boiler rebuilt.
Still exactly the same fault.
Both coils tested & good resistance 35v being sent by board so all ok there. Gas pressure 23mb but noticeably no drop when the boiler was trying to fire. I would have expected a good 1 or 2 mb drop when trying to fire so deduced that the gas valve had also failed. Fortunately had a spare in the van which does several of the Worcester range.
Factory reset as a start point & apart from 440ppm it fired.
All adjusted to book Co2 settings.
In all about 5 hours including merchant visit.
So the fault sheet was more or less correct in that all those things were wrong with the exception of the pcb.
A bit unusual to get 3 parts fail at once, fortunately the customer was perched on my shoulder & could see each faulty part as they were uncovered.

Regards

Arthur
 

Reply to Boiler Breakdown Sticky in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Had a call to a 82 Old man, he paid these £300 up front for a years cover, and I find out on arrival he's been waiting for 3 weeks, no heating or...
Replies
3
Views
600
J
On a breakdown which is stumping me. The boiler has no power to it even though everything else in the system is working as it should. The 3 way...
Replies
3
Views
609
Deleted member 120897
D
I have a clients oil Grant boiler I fitted last year. It is a Vortex pro 26-46 system. It is just a small system loop as it is a pool boiler...
Replies
6
Views
85
Hi do we need to do a gas rate or heat input when doing a boiler breakdown? Thanks
Replies
1
Views
888
G
Tiffel 20-50 boiler will not fire up. Screen shows ambient temp approx 20 degrees with a symbol of a flame. Got the settings just for hot water.
Replies
1
Views
69