before you start any fault finding check the three esentials
pressure
is there water in the boiler dont trust the guage whack half a bar in ive had many gauges reading 1bar when theres realy nothing in it
power
is there power to the boiler
gas
is there definatley gas at the boiler once spent 20 mins to find a fault and the the gas valve under the boiler was in the off position always best to crack a union or put a guage on
Biasi M96(24/28)SM/C2
Round black APS
boiler fires up for a few seconds then goes off, continues to spark. After a few attempts the lock out led comes on. Works when the combustion chamber is off.
check flue was fitted correctly as the white seal bends when pushing the elbow into the flue and doesn't sit right.
Fault only starts after the warrenty period is over
Remove the complete flue clean and pour water in the top of the boiler to clean out the heat exchanger. Done 3 of these in the past year.
Here's 1 for commercial oil burners. I'd say Croppie's seen this. Have seen this happen a couple of times on Riello RL burners.
If the plant room door is open on a sunny day, sun shining in can make d burner go to lock out.
Photocell can pick up light shinning down boiler sight glass, say when boilers up to temperature, photocell picks up some light, the panel thinks there's a flame like a big lump of carbon on d head burning, and locks panel out.
You'll go out on call, Murphy's law it'll be a dull day and there'll b no apparent fault.
You wanna read that again!
You're advising for a expansion vessel to be fitted on the return yet you had a nightmare when you fitted it on the return!!