Recent install Firebird 26kw Condensing boiler. Space heat only. Installed as replacement boiler in well insulated 80s renovated home. (Silver bead wall cavities, triple glazing 0.6 centre pane U value, 450mm rockwool in loft) This house is now split into 2no zones. Downstairs and Upstairs. Independent time & temperature zone controls.

The system design would have been prior to these new condensing boilers. Therefore rads etc would have originally been sized per 82c supply and 71c return as the old tried and tested favourite say.

Whereas it is said that in order for a condensing boiler to condense the system design should be 65c supply, 45c return ideally. No issue for a new build with under floor heating etc. But for an older property like mine this is what I want to explore and talk about in detail.

Would I be correct in thinking the ideal scenario here would be to review the original radiators, delta temperature calculate the output and most likely have to upsize most all of them by factor of 1.5 etc in order to produce effective heat output in the cooler months, whilst reaping full benefits and efficiency of a modern condensing boiler?

I am NOT a heating engineer. I am a chartered Architectural Technologist by trade and Design Manager in daily job. I require to have sound knowledge in all building elements – and to me this includes heating system design. Today I am conducting an initial experiment on my home. To measure over time:

Run time
Condensate output in ML
Boiler Flow & Return Temps
Flue Temp

I want to see generally that if I run the system temperature in a real world example over the 45c to say 55 & 65c return temps that I need to input useful heat to my home, is the boiler still producing condensate and is the flue gas temp also rising indicating loss of efficiency.

Mods can move this to the Oil / Solid fuel section if they like but it is a gerneral condensing central heating discussion and probably will get more exposure in the central heating section.
 
So avoid white LED’s?

Yes I think for a dwelling it is best to avoid white LEDs personally. For Offices and Commercial uses White are great however.

2700 - 3000k is what I aim for.
1646462601697.png

I do have a pre payment type Electricity Meter in my house. Electricity prices went up here in Jan. But before they did I topped up £300. For only two of us in the house we tend to go through alot of electricity..... depite using delay settings on washing machines at night etc too on the cheaper economy 7 rate.

I had about 50% of my house on LED lights until recently. Then I updated the remaining bulbs to all LED warm white. Some rooms like the hallway had alot of bulbs so the 90% savings multiplied by over 10 bulbs would add up.

And certainly knowing how much we normally consume and checking the meter reading since (Which is just a £ remaing figure in a small display in the Kitchen) it appears swapping the remaining bulbs and probably the ones that get the most use has made a marked imrovement in savings. More than I would have thought I mean. Will know better after a few months and when doing Tax return (Which makes me go through utility bills) but could be saving 50p per day.
 
I ended up going with warm white LED lights throughout the interior of my house.
About four or five years ago, after some experimenting with types and makes I went for Philips 2700K LEDs throughout and they're great. In a couple of places I have the dimable ones and these reduce the colour temperature as you dim them (getting a touch more orange at lower levels), which is a nice touch. The whole exercise paid for itself in about 12-18 months.

I'd strongly recommend you only choose between traditional brands (Philips, Osram, etc.) because the cheaper 'own brand', eBay, etc. samples proved to have a bad colour spectrum, be unreliable and, in one case, dangerous.
 
I just purchased one of these smart Oil level monitors. It can determine the estimated run out date and chart oil Consumption trends. Will install it Saturday evening and see how it does over the next while. Much more reliable than depending on myself to look into the tank!

20220318_112356.jpg
 
Hi @JC22024 again. I've been reading through a printed-out copy of this thread and regarding post #92, I feel a need to correct your misunderstanding of how smart pumps generally work. A proportional pressure pump (including Grundfos Autoadapt) seeks to keep the pressure drop constant across the radiators. It very slightly drops the pressure as TRVs close to try to compensate for the decreased pressure losses across the boiler primaries (so there is some truth in your understanding) but one TRV shutting should not cause other radiators to fall dead. It does not drop the pressure very much. Conversely, a 'dumb' pump cannot help but increase its pressure as TRVs throttle down, thus forcing more flow through any TRVs that remain partially open, sometime resulting in whistling. They (smart pumps) aren't without issues, particularly as the conventional automatic bypass valves often fitted to heating systems rely on an increase in pressure to open up as TRVs are shutting down.

Constant pressure will keep the pressure constant across the boiler (but not compensate for the primaries: that's the difference, plus CP is usually a much higher pressure setting).

The way most smart pumps do this is by monitoring power consumption to get an idea of how much drag is being created and then varying the speed of the impeller. Unlike the older pumps which ran at a fixed speed.

I've balanced my own house before and after replacing a pump. The new pump has proportional pressure and I thought I'd give it a go. It actually made balancing MUCH easier as, when I throttled back one radiator, that didn't then result in an increase in pressure and hence flow to the remaining radiators. So instead of going around the house several times tweaking as I went, I only really needed a couple of passes.

Re post #152, I wonder if you could help me follow your explanation better? Please let me know if I follow your understanding correctly or not... you say you think the Vector BEM works by allowing the boiler to first run to temp [i.e. until the boiler cuts out on its internal thermostat?] and then, [when the boiler decides to re-fire?] slightly delays [the next firing up of the boiler?] and then continues doing this while also monitoring the run time and stat call time? Which stat are we discussing? Room stat, I assume?

Are you saying that your understanding is that the BEM is monitoring the boiler duty cycle and delaying the boiler from firing for progressively longer times until it notices that this is reducing the system's ability to get the room temperature up to the required temperature? I'm struggling to get my head around how this works, but it would be interesting to be able to do so.

Thank you.
 
Hi @JC22024 again. I've been reading through a printed-out copy of this thread and regarding post #92, I feel a need to correct your misunderstanding of how smart pumps generally work. A proportional pressure pump (including Grundfos Autoadapt) seeks to keep the pressure drop constant across the radiators. It very slightly drops the pressure as TRVs close to try to compensate for the decreased pressure losses across the boiler primaries (so there is some truth in your understanding) but one TRV shutting should not cause other radiators to fall dead. It does not drop the pressure very much. Conversely, a 'dumb' pump cannot help but increase its pressure as TRVs throttle down, thus forcing more flow through any TRVs that remain partially open, sometime resulting in whistling. They (smart pumps) aren't without issues, particularly as the conventional automatic bypass valves often fitted to heating systems rely on an increase in pressure to open up as TRVs are shutting down.

Constant pressure will keep the pressure constant across the boiler (but not compensate for the primaries: that's the difference, plus CP is usually a much higher pressure setting).

The way most smart pumps do this is by monitoring power consumption to get an idea of how much drag is being created and then varying the speed of the impeller. Unlike the older pumps which ran at a fixed speed.

I've balanced my own house before and after replacing a pump. The new pump has proportional pressure and I thought I'd give it a go. It actually made balancing MUCH easier as, when I throttled back one radiator, that didn't then result in an increase in pressure and hence flow to the remaining radiators. So instead of going around the house several times tweaking as I went, I only really needed a couple of passes.

Re post #152, I wonder if you could help me follow your explanation better? Please let me know if I follow your understanding correctly or not... you say you think the Vector BEM works by allowing the boiler to first run to temp [i.e. until the boiler cuts out on its internal thermostat?] and then, [when the boiler decides to re-fire?] slightly delays [the next firing up of the boiler?] and then continues doing this while also monitoring the run time and stat call time? Which stat are we discussing? Room stat, I assume?

Are you saying that your understanding is that the BEM is monitoring the boiler duty cycle and delaying the boiler from firing for progressively longer times until it notices that this is reducing the system's ability to get the room temperature up to the required temperature? I'm struggling to get my head around how this works, but it would be interesting to be able to do so.

Thank you.

Thanks for that, yes I would agree I don't fully understand the Smart Pumps! Its quite likely my Grundfoss one was faulty too. The regular type pump has been fantastic so far so I don't need to test the pumps any further but no doubt smart pumps have advantages yes.

Ref the BEM, it only has 2no inputs.

1st input is a live feed which is the boiler call signal. Aka the live feed from the room stats which powers the boiler and pump in my conventional system.

2nd input Is from the call side of the boiler thermostat.

That's it. It has no other sensors or data from indoor or outdoor temperatures.

First time the boiler fires up for the day the BEM gets its power feed and starts and also sees how the boiler is firing until the boiler thermostat is satisfied and shuts off. BEM is still live and monitoring from the boiler call feed. Then the boiler stat begins to call again and the BEM delays the burner from firing for a short time then let's it fire until the boiler stat is fully satisfied once more. Watch the video below to see this cycle:


The BEM continues to monitor and log the boiler firing cycles and delaying them more and more until it is effectively matching the system demand over time. (At least this is my understanding of it) Then once the room thermostat / heating call signal stops the BEM and boiler stops and will start from scratch again the next time heating is fired up.

What I like about this particular one is it always let's the boiler thermostat fully satisfy and turn off before it then delays it firing up again. Therefore the comfort inside the house is unaffected as the water temperature does reach full stat just that it will be dropping lower in between boiler firing cycles.

What I will say thinking about this more in recent weeks is the clocks it is showing are accurate in that it is recording boiler stat call time and the boiler burner time (which it reduces) but it's not really accurate to say this is a xx% saving in oil.

Its more of a meter showing how much it has delayed the burner. So the % of oil saved is lower than what the clocks state but it is definitely reducing the boiler cycling as much as practical so this is its main purpose and advantage.
 
@Ric2013 your comments about PP and CP are bang on, so no need to elaborate further there.

With regards to the controller it does exactly how you picture it and is actually quite an intelligent and sophisticated unit.
The heat source in question is an oil boiler and as I’m sure you are aware 99% of domestic oil boilers currently installed are fixed rate output (there are now a couple boilers on the market that one fully modulates and the other is a two stage burner).
The problem with fixed rate burners is unless the outdoor temperature is at design temperature (say -2°c, depends on location) then a fixed rate burner will always cycle and the warmer it is outside the greater this cycling is. This particular unit will monitor and I assume learn these cycle rates and prevent unnecessary firing cycles. Let’s say it’s a 20 kw load at -2°c and a target room temperature of 20°c but the outside temperature is 11°c. You now only require half the output and you would find the burner will run for say 5 minutes and off for 5 minutes while maintaining your internal temperature. The problem is though during that burner off period the flow sensor will notice a drop in temperature and bring the burner on while the rooms are at temperature and try’s closed. This then only circulated water through a bypass or heat sink, the water doesn’t displace any energy and in turn the boiler cycles more. Constant stop starts for any heat source are not good and I know you know why. This unit can minimise this cycling, not only saving fuel but also extending the life of burner components.
 