I am currently planning a kitchen lay out, which may involve replacing a combi boiler to a position next to a window. How close to a window can a flue be installed? If the window is constructed so only one side is opening, is this distance measured to the opening in the building (i.e fixed window), or the actual window opening? Make/Model of boiler is not determined yet, so cannot check MI instructions
 
Last edited by a moderator:
Whatever MI's say, they can't take precedence over building regs (in this case Part J Combustion appliances). It's no great surprise that MI's nearly always just reprint the relevant pages of the regs.

The pages below are taken from the latest issue of Part J. Note the horizontal distance of the flue opening from an opening window of 300mm - this is edge of opening to edge of flue.

See also Note 1:
"An opening here means an openable element such as a window, or a fixed opening such as an air vent. However, in addition, the outlet should not be any nearer than 150mm (fanned draught) or 300mm (natural draught) to an opening in the building fabric formed for the purpose of accommodating a built in element, such as a window frame"

Whatever the MI's say, they can't be less stringent than the building regs and as an installer making holes in buildings for flues, you must take account of the building regs in addition to any MI's. The regs are free to download - it's worth taking a look: Planning Portal - Part J (Heat producing appliances)

flue1.jpgflue2.jpg
 
Last edited by a moderator:
3 assesors have told me from the center of the flue thats why im a tad confused
Nobody has told you this, you have misunderstood ...it it always from the outside edge and if you don,t no this simple thing you could do with a refresh course.
 
are you saying that to measure the distance of the flue from the opening you put your tape at the window edge and take it to the end of the flue and measure that distance ?

you take your measurements from the closest 2 points of the 2 things you are measuring between then any other dimension is "safer" what do you mean by "end" this end or the other end, i say the closest points which is clear (or so i thought haha)
 
if everyone is so sure could someone please tell me exactly what regs state word for word

i think you need to clarify with the 3 assessors who have given you duff info (bet you dont get an email from them saying it is centre of flue) TBH a lot of info gets clouded and once clarified you will be fine with it, and as i suggest to most gas folk 9/10 invoke common sense and you will understand as in this instance it makes no sense to take a generic safe dimension from the middle of the flue as this will make larger flues more dangerous than small ones, so always nearest to nearest dimensions, and the place to get all your flue info is BS5440-1, which im sure you can access somewhere
 
sorry to go back to this guys but think about it if you measure from the center of the flue it makes no difference what the diameter of the flue is you are always measuring from the same point

you are scarting me with this one, back to basics here:
the minimum dimension is to minimise/control if you like the amount of POC's which may get back into the building, a clever bod somewhere has said if the flue is no closer than 300mm it will be safe (a discussion for another day methinks) so you are saying that a calculated amount of POC's from a 100mm flue is xcm3 and by measuring from the centre we can work out what x is, but if you then have a 200mm flue and measure from the same place you will get the same amount of POC's being near the opening, draw a straight line down the side of an A4 sheet for the wall then draw 4 dotted lines horizontally away from the wall and mark them at 300mm, then draw a horizontal line down thro' the 300mm dotted lines, now take the scenarios we are discussing, the top one draw a 100mm dia circle at 300mm centre to the wall, the next one down draw a 200mm circle with centreline at the 300mm line then the third one down draw a 100mm circle with the inner edge touching the 300mm line, then on the fourth draw a 200mm circle with the inner edge touching the 300mm line, then see if this makes sense and hopefully it will clear up your misconception on whether it matters what size the flue is when you do it from the centre (and therefore why it is wrong) and by my reckoning measuring from inner edge of ANY circle means every one of my flues conforms
 
Whatever MI's say, they can't take precedence over building regs (in this case Part J Combustion appliances). It's no great surprise that MI's nearly always just reprint the relevant pages of the regs.

The pages below are taken from the latest issue of Part J. Note the horizontal distance of the flue opening from an opening window of 300mm - this is edge of opening to edge of flue.

See also Note 1:
"An opening here means an openable element such as a window, or a fixed opening such as an air vent. However, in addition, the outlet should not be any nearer than 150mm (fanned draught) or 300mm (natural draught) to an opening in the building fabric formed for the purpose of accommodating a built in element, such as a window frame"

Whatever the MI's say, they can't be less stringent than the building regs and as an installer making holes in buildings for flues, you must take account of the building regs in addition to any MI's. The regs are free to download - it's worth taking a look: Planning Portal - Part J (Heat producing appliances)

View attachment 4961View attachment 4962
as i understand it mi' over rule everything building regs get changed at long intervals new products get tested and approved daily
 
as i understand it mi' over rule everything building regs get changed at long intervals new products get tested and approved daily

Your council building control officer won't give a monkeys what MI's say - he'll inspect against Part J unless Part J refers to MI's or other standards (which happens only in very rare circumstances - height of flue openings above roof intersection being an example).

In the end it doesn't really make much difference as MI's will never specify a more lenient dimension (they use the regs as their baseline when writing their own instructions and they will include a statement such as 'these dimensions comply with current building regulations').

Ultimately however, the current building regs take precedence over MI's
 
Last edited by a moderator:
looking through the IUP they state the following as the chain of command for info compliance

H&S at work act
GSI&UR
Building standards or regs
specific MI
relevant BS docs
other industry codes of practice etc
 
So to answer the guys initial answer, if other clearances are met he may be able to be 150mm away from the window and fit a pluming kit.
 
looking through the IUP they state the following as the chain of command for info compliance

H&S at work act
GSI&UR
Building standards or regs
specific MI
relevant BS docs
other industry codes of practice etc

MI instructions over ride everything else.
 
Nope.
Just as previously written they don't overide H&S, GSI and building regs
I think you are wrong.. I have always been told MI over ride everything else and this is what we trained out at BG
 
I think you are wrong.. I have always been told MI over ride everything else and this is what we trained out at BG[/QUO

have a read at your IUP, i have listed the info as it is listed there, and remember the building regs will reference the MI but one that springs to mind is flues next to a boundary of a semi detached borderline, if you quote MI the flue needs to be 300mm from an opening, so you fit the flue on your side of the fence (obviously) and measure and confirm it is 400mm from next doors openable window so you have complied with the MI next door complain to you about the "white smoke" entering their prop, you tell them its nothing to worry about as anything over 300mm is safe, they say "aye right i'm away to the cooncil" who do you think the building control will agree with? (i know they will agree with the neighbour and can issue a non-conformity order making you move the flue, so who's the daddy? the MI or the local building regs?
 
have a read at your IUP, i have listed the info as it is listed there, and remember the building regs will reference the MI but one that springs to mind is flues next to a boundary of a semi detached borderline, if you quote MI the flue needs to be 300mm from an opening, so you fit the flue on your side of the fence (obviously) and measure and confirm it is 400mm from next doors openable window so you have complied with the MI next door complain to you about the "white smoke" entering their prop, you tell them its nothing to worry about as anything over 300mm is safe, they say "aye right i'm away to the cooncil" who do you think the building control will agree with? (i know they will agree with the neighbour and can issue a non-conformity order making you move the flue, so who's the daddy? the MI or the local building regs?

MIs will also add that all important get-out clause that plume must not cause a nuisance; therefore if plume is causing a nuisance even though you have adhered to MI's clearances, you have still contravened MIs.
 
I think you are wrong.. I have always been told MI over ride everything else and this is what we trained out at BG[/QUO

have a read at your IUP, i have listed the info as it is listed there, and remember the building regs will reference the MI but one that springs to mind is flues next to a boundary of a semi detached borderline, if you quote MI the flue needs to be 300mm from an opening, so you fit the flue on your side of the fence (obviously) and measure and confirm it is 400mm from next doors openable window so you have complied with the MI next door complain to you about the "white smoke" entering their prop, you tell them its nothing to worry about as anything over 300mm is safe, they say "aye right i'm away to the cooncil" who do you think the building control will agree with? (i know they will agree with the neighbour and can issue a non-conformity order making you move the flue, so who's the daddy? the MI or the local building regs?

white smoke ok, he's celebrating the appointment of a new pope.
 
Thers some vain people on here.

Think you mean there are some very knowledgeable members who are willing to spend their time explaining to others the correct way to interpret regulations and correct industry procedures

The items brought up here are important and should be understood correctly by those in the trade

Please keep on topic and away from cheap, unsubstantiated remakes

Thank you
 
I think you are wrong.. I have always been told MI over ride everything else and this is what we trained out at BG[/QUO

have a read at your IUP, i have listed the info as it is listed there, and remember the building regs will reference the MI but one that springs to mind is flues next to a boundary of a semi detached borderline, if you quote MI the flue needs to be 300mm from an opening, so you fit the flue on your side of the fence (obviously) and measure and confirm it is 400mm from next doors openable window so you have complied with the MI next door complain to you about the "white smoke" entering their prop, you tell them its nothing to worry about as anything over 300mm is safe, they say "aye right i'm away to the cooncil" who do you think the building control will agree with? (i know they will agree with the neighbour and can issue a non-conformity order making you move the flue, so who's the daddy? the MI or the local building regs?


M.I are right, as they say, follow their dimensions but only as long as it does not cause nuisance, so MI were right.
When we go and fit a boiler we follow the M.I as this is what we are given to do the job. These are written so that they include all relevant regs we need. Some B Regs we need to know like sleeving gas etc, but it does not override M.I as they dont explain how to get gas there only what is required.
 
i read two pages of this before i realized id read it before please stop resurecting old posts
 
Status
Not open for further replies.

Reply to How close can a boiler flue be to a window? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

D
Replies
4
Views
2K
davevincent
D
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock