Compact 35He solid red lockout.

Discuss Compact 35He solid red lockout. in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Status
Not open for further replies.

GrahamM

Plumbers Arms member
Plumber
Gas Engineer
Messages
2,045
Last job tonight.
2 year old compact he, fan running, aps proving, NTC/overheat stats OK, condi trap clear.
Switch on power, fan runs then goes to solid red, fan keeps running.
Is there anything else I may be missing before picking up a new board?
 
No spark at all. As soon as power put on, fan starts, aps proves and goes to red lockout within 2 seconds. Nothing else.
Did not check power to gas valve.
 
How does reverse polarity happen? Is it something that's always been wrong ie wired wrong and never caused a problem or some fault with the electrics that causes the switch?
 
How does reverse polarity happen? Is it something that's always been wrong ie wired wrong and never caused a problem or some fault with the electrics that causes the switch?
Normally by sparkies getting the polarity wrong when they renew the fuse box. I've seen it at least three times.
 
another good cause of RP is diyers messing with electrics adding extra points,spurs etc and reversing live and neutral or earth
 
Was the board!
Unbeknown to me the new board has changed and now requires the separate ignition board as well. The original board was one unit with the ignition module self contained.
 
Status
Not open for further replies.

Reply to Compact 35He solid red lockout. in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock