A vessel installed 4M away from the cylinder is very unlikely to be the right side of a check valve if it is on the cold feed.
Could it be there for another reason other than expansion ?
I diagram would be useful as I am struggling to understand what is going on from your description Duker996.

Good point Chris, I overlooked that
 
At which point did I say I don't have the G3 qual? I do have the qualification and understand exactly how all the parts work. I have just never encountered this problem before so asked for advice, which I'm never too proud to do. Don't be so quick to judge chaps!

I think you may have nailed it Best, turns out the issues started after they had a new bathroom fitted so my guess now is no check valves on the feed to the new shower.
You didn’t say that you was G3 registered either!
 
A vessel installed 4M away from the cylinder is very unlikely to be the right side of a check valve if it is on the cold feed.
Could it be there for another reason other than expansion ?
I diagram would be useful as I am struggling to understand what is going on from your description Duker996.
Maybe it's a megaflo?
 
That would be my guess! If expansion vessel is 4m away, more likely to be heating expansion vessel rather then hot water.
The OP has their G3 so I would expect them to be capable of knowing the difference between heating & hot water vessels.
20190305_141608.jpg

Even if it is a Megaflo with an internal air bubble for expansion addition vessels can & are often added, for instance when the baffles has failed or there is a secondary return installed which increases the amount of water being heated.
The worry here (as far as I can tell from the description) is that it has been installed on the cold feed 4 Metres away from the cylinder so it is very likely to be on the wrong side of the check valve which is built-in just before the pressure relief safety valve. If it is then this will isolate the vessel from the source of expansion so it can't work & the pressure will continue to cause the safety valves to open!!
 
All sorted now chaps.

As Gary said it was due to not having balanced supplies at the new shower and them clearly not fitting check valves. There was no way of me getting to any of the shower pipes so a 3bar pressure reducing valve on the incoming main has cured it.

No idea why the vessel, relief valve, reducing valve etc was placed in a small roof space 4 metres away but it is all correct and how it should be, no check valve between the vessel and cylinder.

First time I've seen this issue in my 19 years plumbing, hence why I was a bit baffled by it!

Thanks all for the help
 

Reply to Adding a second Expansion Vessel? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4...
Replies
9
Views
464
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock