B
Blackcatgas
Further to my other post about floor vents..... I went to a job today, the dfe fires been capped, the paper work says 100cm2 vent required, its a 10.2 kw fire, Ive calculated that it needs a 15cm2 vent, the installation instructions concur with this. Is there some new reg that I dont know about that says all dfe fires must now have a 100cm2 vent as a matter of course now?.