300mm from the opening in the building. So edge of brickwork.
ok let me try again flue to window when closed 300mm when window open the sash is then 100mm away from flue?......
ok let me try again flue to window when closed 300mm when window open the sash is then 100mm away from flue?......
ok let me try again flue to window when closed 300mm when window open the sash is then 100mm away from flue?......
You are confusing the issue,
First things first it doesn't matter if the window is open or shut, the criteria is "can the window be opened or is it a dead light"
If it can be opened the flue must be more than 300mm from the opening, if it is dead light the flue must be 150mm from the fabric opening which is where the frame joins the brickwork, however just to throw a spanner in the works, the measurement should be taken from the edge of the flue, not the air intake pipe
kirk, do you happen to know where this is outlined in writing? I have alway said it is from the exhaust of the flue where others have argued it is from the intake. I'm sure I have seen it mentioned though that the window should be measured from the fabric opening although I don't agree with it myself, something to do with the window being replaced and the dimensions changing.
Would be good to get some clear clarification on this.
its from the outside of the flue (air intake) unless the manufacturer allows it to be closer when its plumed away. Normally 150mm with most manufacturers which is the min you must be away from the opening to avoid weakening the structure of the wall and stick to building regs. the reason its best to keep to the fabrics opening is to avoid having to prove you did right before a window was changed. whos to say a builder wont come along and alter whatever? you cant win sometimes.
The flue is parallel with the wall the window is in?
And the opening sash gets closer to the flue when it's opened?
If so the flue always stays 300mm from the opening in the fabric of the building, just the sash moves closer.
I wouldn't be happy with that personally. Years ago we used to screw windows shut and say they were not openable, we were told by corgi that was not acceptable.
Again its a bit of a grey area but you could argue that the window is facing a terminal at its furthest point. I would be doing a co room test with the boiler on full and the window open.
Who's to say a builder won't come along and cut a new opening or build a conservatory over the flue. All you can do is fit it to the regulations, you cannot be responsible for the actions of others after you have finished the job. If there is any doubt take a photograph.