Went back today and changed the seals on the fan and burner also noticed the ceramic bit of the burner was loose so fitted a new burner but after 15 mins of running it cuts out again off the limit stat on the fan but it runs with the front off mmm back to the drawing board it’s a shame the...
boiler goes to overheat lockout if you let it cool and press reset it works for 15 mins then locks out again, it also makes a noise like a foghorn for about 5 to 10 seconds at ignition i have checked all limit stats all are ok also replaced the combustion door seal, cleaned the burner it does...
Went to service worcester 18 ri found the casing red hot the burner seal had gone so decided to do a strip down service as the fan pressure was -4.
Removed fan bum, burner, top baffle but could not get bottom baffle out was on with it for 3 hours tried bicarb and water as Worcester said this...
Hello heating gods I am a Vaillant approved installer and until lately have considered Vaillant to be the best on the market this week I have had 3 boilers go down with f75 Vaillant say its sludge but one of the boilers was only installed in September, when we install our boilers we do a power...
Been calling around about doing subbie work rang a guy that said back boiler to combi fitting vokera vision he has terms that gets him them all in for £695 you buy the pack and fit it then he pays you £1000 I unintentionally laughed down the phone he said is wrong we have loads of plumbers doing...
I agree up to now I have always fitted vaillant with power flush and Magna clean but all this get a free boiler **** seems to have taken all the boilers as even if people are not able to get the free boiler they get the free boiler company out to see if they can get it and once they are in they...