  1. P

    2 zone CH but 1 zone heats whole house

    Thanks again for all the help with this - firstly the pipes. Yes they are both hot both above & below the valve. The plumber came back again today (I think it’s his 4th visit!). He’s suggested that both of the valves (the ones that switch from A to B) have been incorrectly fitted, so hot water...
  2. P

    2 zone CH but 1 zone heats whole house

    I spoke to soon! The downstairs thermostat just called for heat to warm up the lounge & kitchen radiators. They’re now hot but problem is - so are the upstairs radiators (where the thermostat controlling the zone is turned off!). We can stop upstairs getting to warm by turning down the TRV’s...
  3. P

    2 zone CH but 1 zone heats whole house

    It’s a Greenstar 30i ErP NG Combi Thanks for all your contributions. The plumber came round again this morning & was here for over 3 hour’s trying to sort it all out. Having pulled up the flooring in the boiler room, he said the return pipe was incorrectly plumbed in & sending hot water...
  4. P

    2 zone CH but 1 zone heats whole house

    Hi Bibbs - thanks for the reply. The plumber has promised to return today so it’s good to have some ideas about what the problem might be. It’s a combi boiler (brand new) - i’ve added a photo of what the system looks like when the downstairs thermostat is calling for heat but the upstairs...
  5. P

    2 zone CH but 1 zone heats whole house

    Thanks for your responses so far. One thing to add - after setting all the upstairs radiators to zero last night, i’ve come downstairs this morning to find all the downstairs radiators barely producing any heat at all. The downstairs thermostat is reading 18c but calling for heat to make the...
  6. P

    2 zone CH but 1 zone heats whole house

    Thanks Scott - I took a photo yesterday (when the downstairs thermostat was calling for heat). As you may be able to make out - one of the motorised valves is on A & the other on B - so I didn’t think this was the problem. But could there be something going wrong inside the unit itself that I...
  7. P

    2 zone CH but 1 zone heats whole house

    I’d really appreciate some advice. We moved into a new build 3 story town house last Monday. It’s got a Worcester boiler & 2 wireless thermostats (one by the front door, the other on the first floor landing). When the downstairs thermostat asks for heat (to warm up the kitchen & lounge) every...