Hi all,
I am wondering if someone can make sense of this. I have been trying to determine if there is a leak on an existing water supply pipe. Attached a dry pressure guage to garden tap and turned tap on. Pressure went to about 3.5 bar then I shut off supply at the water meter. Over the next hour pressure dropped to around 2.5 bar. I assumed there was a leak but could not find anything. Next day I took a meter reading and 5 hours later there was no change at the meter, indicating no leak! I have tested the pressure guage independently with a stop end and pump and seems to hold.
Very confused, what am I doing wrong and is this the correct way to test a supply pipe?
 
If you have any 'plastic' pipe in the setup you may be seeing the effects of this 'relaxing' after a the change in pressure.

A tricky point about testing in the way you are doing is how to rule out the possibility that the isolating valve at the meter end is not drop-tight.

The pressure in a sealed rigid container filled with water is very sensitive to leaks, changes in temperature and deformations of the container. I wouldn't personally worry too much about transient changes in pressure of the size and timescale you have described.

I'd suggest using the water meter observed over several hours to establish wheter you have a leak and only switch to pressure drop-rate measurements to pin down where the leak is located.
 