Hi All,
Really not sure if this is the right place to post this but I'm in a bit of a mess with my mum's energy supplier and I'm desperate for someone who knows what they're talking about to help.

End of last October my mum rented a two up- two down semi detached relatively modern house (decently double glazed and insulated) near me. Everything in the property is electric apart from the central heating boiler which is quite old (it's a Stelrad Ideal W 2000).

The energy company, Spark energy started her direct debits off at £65 a month. At the time I thought this was maybe a little high and figured we would get it down a bit once we had some meter readings.

Last week Spark wrote to her saying that the direct debit was going up to £95 a month at which point I went through the bills with a fine tooth comb.
Anyway, to cut a long story a little short, I've calculated that in the 138 days mum's been at the property (admittedly over winter) according to the meter reads she's used 671 cubic metres of gas or 7,506 kwh which works out at 54.3 kwh per day average.

My question is this, does this seem like high usage given that she only has a single thermostatically controlled boiler?

Any help greatly appreciated. Thank you in advance.
 
did you actually record the meter readings at the start as spark engy doesnt have the best rep if your asking me

in short high charging and over charging are the main two also not reading the meter and very high estimations etc
 
Is that figure (£65/95) for both gas and electric combined? Some Energy Co's want you to build up credit over the summer months to cover winter energy use but your mum obviously couldn't do that. I'm assuming the Energy Co may have based the increase on the last four months use in which case it's going to be a bit high until her use decreases in which case you can get back to them. Personally I hate monthly direct debits and prefer to pay for what I've used every quarter but appreciate not everyone can do that. They probably have a variable tariff that adjusts with your readings, I'd consider that or they'll continue to want to change things.
 
Hi, thanks for your reply. Yes, I recorded and photographed the meter when she moved in.
I suspect the meter may be faulty but Spark says they will charge us £200 if it's tested and found to be OK.
That's why I wanted to ask some experts if 671 cubic metres of gas over four and a half months or averaging 54 kwh per day seemed like too much.
 
Yes the bill is a dual fuel charge. I was wondering if anyone knows anything about a Stelrad Ideal 2000 W boiler and if it was possible for such a device to use 54 kwh per day even if it was on full blast.Like I say, I have a strong suspicion the meter is faulty, but am not expert enough to know if that particular boiler isn't just inefficient (being old) and using a whack load of gas.
 
Hi All,
Really not sure if this is the right place to post this but I'm in a bit of a mess with my mum's energy supplier and I'm desperate for someone who knows what they're talking about to help.

End of last October my mum rented a two up- two down semi detached relatively modern house (decently double glazed and insulated) near me. Everything in the property is electric apart from the central heating boiler which is quite old (it's a Stelrad Ideal W 2000).

The energy company, Spark energy started her direct debits off at £65 a month. At the time I thought this was maybe a little high and figured we would get it down a bit once we had some meter readings.

Last week Spark wrote to her saying that the direct debit was going up to £95 a month at which point I went through the bills with a fine tooth comb.
Anyway, to cut a long story a little short, I've calculated that in the 138 days mum's been at the property (admittedly over winter) according to the meter reads she's used 671 cubic metres of gas or 7,506 kwh which works out at 54.3 kwh per day average.

My question is this, does this seem like high usage given that she only has a single thermostatically controlled boiler?

Any help greatly appreciated. Thank you in advance.

Hello Gareth Peters,

54.3 Kw hours only works out at just over £2.08 per Day including Vat at the rate that I pay for Gas - 3.8325p per Kwh inc. vat - that is not including the Standing charge.

At that rate of consumption your Mum`s Gas bills would be covered by about a £70.00 per Month Direct debit for Winter / Autumn quarters.


But obviously She would not be using anything like that amount in the Spring and Summer quarters so that Monthly amount should not be charged for all 12 Months.

When You write that She only has `a single thermostatically controlled Boiler` what about the Radiators that the Boiler heats - are the Radiators on throughout the House ?

Any idea how many Hours per Day your Mum has been using the Heating system ?

Considering most of the usage has been during the Winter quarter - for example 6 or 8 Hours per Day would be reasonable `value for money` for just over £2.08 [34.6p or 26p per hour] not including the Standing charge - this is obviously just a `Guesstimate` for a Modern - medium sized - Double glazed & well Insulated House.

Is there Loft Insulation ? - the recommended thickness is now 260mm - made up of 2 x layers - the top layer laid at 90 degrees from the bottom layer to prevent `Cold Bridging` through the Ceiling joists.

As Member Shaun mentioned You should definitely keep a close watch on your Mum`s Gas Meter readings.

You have been able to calculate the Kilowatt hours from the Cubic Metre usage so why not do some checks by noting the Meter reading before your Mum turns on the Heating - note how many hours that it is On - read the Meter again and calculate the usage / Kwhrs - divide that by how many hours of use and work out how much per hour the Heating has cost to run.

The Calorific value [you already know that] and Kwhr cost will be on your Mum`s Bill hopefully - or perhaps on yours if Direct Debit Customers do not get itemised quarterly Bills.

I have read online that there is some really Cold Weather coming to the UK this weekend - `The Beast from the East 2` - if the temperatures are as low as I have read the weekend would be a good time to do the Gas usage tests and calculations.

Regards,

Chris
 
Last edited:
I was just going to say do 24/48hr meter reading test this weekend as it's going to be cold, that'll give you an idea of what her (max) usage will be per day.
 
£2 a day is not a lot. It is surely more important that she is warm and safe than fretting about a few bob. Pop down the Poundshop and check out the price of a bag of fuel. If she qualifies, a basic winter fuel allowance would pay for 100 days, most of winter.
A 28kw boiler could use 56 kWh in 2 hrs...
 
Don't forget these old boilers have a permanent pilot that is on 24/7
this boiler is out of the ark, you need to find out if she qualifies (or landlord) for a free boiler upgrade
 
Thanks for everyone's help and suggestions. I'm going to keep a close eye on the usage while at the same time switching away from Spark (expensive, poor customer service).

Once she's switched I'll get her a smart meter installed. Also, it looks very likely she'll qualify for a boiler grant and as far as I can tell the landlord can't refuse to let her upgrade to a modern boiler.

Thanks again all who replied.
 
The problem with smart meters is that many people get obsessed with watching the darned thing. I have had elderly customers getting very stressed out watching their smart meters. They end up worrying about it all the time when they didn't before and often turn off their heating when they really should be warm. Not saying your mother will be like this but it's something to bear in mind.

Personally I hate the things.
 
Never had a smart meter. But I have used an energy monitor. Useless bit of kit - it couldn't take power factor into account so it thought my fluorescent tubes were using 110W, not 55W. Also, the idea of setting an alarm if you were using more than a certain amount of power was good, but obviously would sound every time the electric shower was turned on.

With regard to the OP's question, I can't check the actual gas input of the boiler in question on the available information, but even an 8kW input boiler (about the smallest you'll find, and probably smaller than you'd need for an end-terrace boiler) will burn 8kWh of gas in an hour if running flat out, and so it really is as simple as gas consumption multiplied by firing hours. If the boiler is running continually, then the thermostatic control won't be switching the burner off.

If the thermostat were faulty, the boiler would overheat and you'd have significant other issues other than excess gas consumption.

If you wanted a quick and dirty test of the meter accuracy, you could try a meter reading to 1 decimal place before and after an hour of the boiler firing constantly (perhaps when it's first switched on in the morning) and come back to us with that (and the GC number of the boiler, if you can find it) and we can tell you if it's plausible.

You tell us you've checked the actual meter readings, so it doesn't sound like an energy supplier mistake (kWh should be approximately equal to cu m x 11).

But, more likely, it's a poorly insulated house, like most UK dwellings, and an inefficient boiler. By law, a rental property will have an Energy Performance Certificate, which should give some indication of the level of insulation etc. What does that document tell you?
 
I just checked the boiler and the GC number is 41 415 87 if it's any help.I can't lay hands on the energy certification info at the moment until I go round to mothers but it "seems" pretty well insulated. The double glazing and doors are well fitted and don't leak, there's a decent depth of insulation in the small loft. My impression from being round there is it's a house that "holds the heat" well, plus of course it's a tiny semi so not much to heat.
 
Everything in the property is electric apart from the central heating boiler which is quite old (it's a Stelrad Ideal W 2000).
There are four versions (30N, 40N, 50N and 60N) of the W2000 with outputs ranging from 8.8kW to 17.6kW, which one do you have? (Inputs vary from 11.5kW to 23.4kW)
she's used 671 cubic metres of gas or 7,506 kwh which works out at 54.3 kwh per day average.
That is equivalent to the boiler running flat out for 5 hours if she has the smallest and 2 hours for the largest.

she only has a single thermostatically controlled boiler
Is there a thermostat on the wall to control the house temperature? If not, how does she control the temperature?

How many radiators in the house?
 
If the spare bedroom isn't in use you could turn the rad down or off via the lock-shield (valve either end of rad) . I'd always hesitate having a "smart" meter installed especially for the vulnerable, guilt meters more like assuming you visit more than once a month and set up her account online I'd do it yourself.
 
We had a new thermostat fitted last month, that works perfectly.There are five radiators, 4 medium sized and a small one in the bathroom. I have the hot water on the timer as it's not an on demand boiler, that comes on for an hour in the morning and an hour in the afternoon. Last time I was round there I photographed the boiler info which I attach below.
20180313_120914.jpg
20180313_120922.jpg
 
8.8kw is about the right size for the house including the hot water cylinder. Sounds like she's had it on for most of the day which you'd expect during the cold spell.
 
Bear in mind that 8.8kW is the output, but due to inefficiency of the system, the probable input (looking at the handwritten note on the label and assuming it is correct) is 27000btu, so it's actually using 10.8kW worth of gas when it is firing.
 
she's used 671 cubic metres of gas or 7,506 kwh which works out at 54.3 kwh per day average.
Assuming the heating is on from 0600 to 2200 (16 hrs) that work out at 3.4kW per hour. The boiler can consume 11.5kW per hour, so it is only alight for 18 minutes per hour.

Does the heating go off overnight? If so it might be worth experimenting with having the heaIting on at a lower temperature (say 16C) overnight. This acts as a 'back stop' preventing the house getting too cold, which is what uses up most of the gas.

Just a thought! Was the last gas/electric bill based on actual or estimated readings? Have you asked the supplier to justify the increased monthly payment(e.g Fixed price tariff ended)?

@Ric2013
Don't you mean 37,000?

 
So from what's being said, the upshot is this boiler could easily use that volume of gas under normal usage in cold weather. Thanks very much all who helped clear that up for me, an old inefficient boiler I can deal with, just glad I didn't foolishly request an accuracy test as Spark were talking about a £200 charge if the meter was found to be ok.
 
£65 for dual fuel looks a bit on the low side ....................

What you need to do is take readings from both lecky and gas every week for a few months ......................

And as for "smart" meters - just don't get them......
 
It has been a very cold winter. My boiler is the latest type and we have our stat set at a comfy 18 degrees which most older people will find cold. My supplier has upped my payments by £30/ month . Get the boiler serviced and a gas rate / burner pressure / combustion checked which ever is relevant for that boiler. This will at least tell you its doing its best. Rest is down to efficiency of the CH system and heat loss of house.
cheers
 
And as for "smart" meters - just don't get them....
On a tangent as it sounds like the OP is now happy, what is wrong with 'smart' meters in your opinion or experience? I don't really see the need (yet), and have some concerns about the radio frequencies used, but other than that...?
 
Hello All,

Without wanting to start arguments some of the comments on calculating the Gas consumption of the OP`s Mum`s Boiler would not produce accurate results.

We must remember that during very cold weather the initial `Heat Up Period` of the first daily use of the Heating / Boiler would probably be close to the Maximum Gas Rate especially if the first hour also included heating the Hot Water Cylinder - but after that the Hourly Gas consumption should be nothing like that.

The hourly Gas consumption to maintain the House temperature might only be 33% of the Maximum Gas Rate because the Boiler might only be firing for about 20 minutes per hour if the House is well Insulated and Double glazed and new Thermostat is positioned correctly.

Gareth / the OP has stated that the Room Thermostat is new and seems to be working correctly.

This is obviously a `Guesstimate` as every property is different - but it would not be accurate to just multiply the Maximum Gas Rate by the amount of Hours that the Heating is On for.

When the Hot Water Cylinder is heated again [late afternoon ?] the Gas consumption will obviously increase for that hour [ Cylinder heated for 1 hour morning & afternoon].

However I am pleased that we have now reassured Gareth that although his Mum`s Boiler is `Old & very Inefficient` that the 54.3 kwhrs per Day that he asked about is NOT a surprisingly large daily amount of Heat for an old Boiler supplying the Heating & Hot Water.

Regards,

Chris
 
Last edited:
The building fabric heat loss is the biggest
Not necessarily. It all depend on the ventilation losses.

My house has a fabric loss of 256W/°C and a ventilation loss of 185W/°C per air change. If only one air change is assumed the total loss is 256+ 185 = 441. The fabric loss is 256/441 = 60%. But if there are two air changes the total loss is 256+185+185 = 626 and the fabric loss is 256/626 = 41%.

Modern houses have much lower ventilation losses as they have to meet strict Building Regulations requirements.
 
On a tangent as it sounds like the OP is now happy, what is wrong with 'smart' meters in your opinion or experience? I don't really see the need (yet), and have some concerns about the radio frequencies used, but other than that...?

My main gripe is that there is currently no one single standard, so if a user wants to change suppliers, they also have to arrange to get their smart meters changed over .................... things are supposed to be changing but .............. hum, when exactly, and then what about all the units installed? As a spark this is my perception of the ones used by the suppliers

Also they need to be renamed - there is nothing "smart" about these meters .................... all they do is make meter readers redundant.

They can't tell you how much single appliances use, nor if such an appliance is energy efficient. Sure the needle may be in the green, but if all you have on is your aged 500w floodlight is that any surprise..................

And then there is the small matters of reports of them not recording usage accurately
 
One big mistake people make when using their heating is to repeatedly turn the heating on for a couple hours, then off a couple, then on again, during each day.
Elderly folk particularly do this, thinking they are saving money.
All this obviously results in is long reheat burn times with much more fuel used and less heat in the property.
I have difficulty trying to explain that to some customers because they see it as if their heating is on at programmer, then fuel is constantly being burned. o_O
 