this came up the other day, I was in the merchants and a guy seen my regin premier gauge hanging up in the van,
he said, you shouldn't be using that gauge, so I said wtf you talking about. he muttered something about not using it with air, but it didn't make much sense, so I done some digging, and here's what I found
There's no problem using these gauges with gas as a medium, but the same cant be said when carrying out a tightness test using air, ie new installs with no meter etc.
now for the boring stuff
every gauge has a grm, ie water 0.5, electronic 0.1, sg 1.
test medium has a constant known as f1, ie f1 gas = 42 and f1 air = 67
ttd is calculated with grm x iv x f1
max domestic iv = 0.035
so water gauge using air = 0.5 x 0.035 x 67 = 1.17 seconds
& regin premier gauge using air = 1 x 0.035 x 67 = 2.34 seconds
the regin gauge would be fine if we allowed 2.34 secs as test duration but considering we use
2 mins, then tightness test would fail
I know it's a lot of pyish, but it's all true pyish, hahaha
he said, you shouldn't be using that gauge, so I said wtf you talking about. he muttered something about not using it with air, but it didn't make much sense, so I done some digging, and here's what I found
There's no problem using these gauges with gas as a medium, but the same cant be said when carrying out a tightness test using air, ie new installs with no meter etc.
now for the boring stuff
every gauge has a grm, ie water 0.5, electronic 0.1, sg 1.
test medium has a constant known as f1, ie f1 gas = 42 and f1 air = 67
ttd is calculated with grm x iv x f1
max domestic iv = 0.035
so water gauge using air = 0.5 x 0.035 x 67 = 1.17 seconds
& regin premier gauge using air = 1 x 0.035 x 67 = 2.34 seconds
the regin gauge would be fine if we allowed 2.34 secs as test duration but considering we use
2 mins, then tightness test would fail
I know it's a lot of pyish, but it's all true pyish, hahaha