Has anyone else come across this situation? I keep detecting products of combustion inside the casing of Ideal Logic boilers. I've replaced every seal I can find, namely flue seals, turret seals, sump connection seals, burner seal, electrode seal, flame detection seal, etc, and yet still I pick up co readings of about 10ppm. I even had the manufacturer come in on a fixed price repair who have also replaced all the seals, and yet when I came back to check I still pick up small co readings. Is this the norm??
 
do they have gas hob, is boiler in kitchen, have you checked room co, have you put new filter in your analizer.
 
Around the top of the burner ? As it’s a know issue and ideal advise using a mirror only and not a fga
 
Around the top of the burner ? As it’s a know issue and ideal advise using a mirror only and not a fga
Yes around that area. So ideal advise not to fga inside around the burner??
Flue integrity test is fine. Readings in the case around the top of the burner are picking up about 10ppm of Co
 
Yes around that area. So ideal advise not to fga inside around the burner??
Flue integrity test is fine. Readings in the case around the top of the burner are picking up about 10ppm of Co
If the analyser is good and it zero's OK so it is definitely not collecting ambient CO, I would personally fail it. You do not know what the leak is or whether it is likely to increase. I would involve the manufacturers if you find this a lot and get them to accept responsibility for it or at least give it in writing that they think it is acceptable.

Just saying what I would do. You can find more than that level in certain work environments short term but it is the 'unknown' element that would bother me.
 
Yes around that area. So ideal advise not to fga inside around the burner??
Flue integrity test is fine. Readings in the case around the top of the burner are picking up about 10ppm of Co
Correct
 

Reply to Ideal logic products of combustion in casing in the Gas Engineers Forum area at PlumbersForums.net

Similar plumbing topics

W
Hi all, I've got a bit of a strange issue relating to my Ideal Logic Combi 35 which has recently started displaying a F2 error when trying to use...
Replies
2
Views
988
Williams25
W
Hi, As per the thread title, I have an Ideal Logic Combi 30 and I am having a problem with the pump, which keeps activating without any DHW/DCH...
Replies
2
Views
1K
  • Question
Hello guys! I had an Ideal Combi Logic+ C24 fitted in August 2021 in my mid terraced house and I started noticing that it was losing pressure...
Replies
9
Views
1K
Hi. I have an issue with my Ideal Logic+ System S24 boiler which I hope someone can help with. Below is as much detail as I can think of. The...
Replies
4
Views
1K
In our Village Hall we have a Ideal Concord CXS/SD40/H central heating boiler. This was installed new when we had an extension built and the...
Replies
10
Views
1K
Back
Top