System boiler tripping RCD at consumer unit

Discuss System boiler tripping RCD at consumer unit in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Messages
5
Hi, I am looking for advice on a system boiler on S plan that keeps tripping the RCD for heating system. Friend called me, she had no power to boiler and called an electrician as the RCD wouldn’t reset. The electrician checked programmer and said it had power to connections and thermostat, but no power to the boiler. The programmer display was flickering and the red leds weren’t illuminated when selecting CH & HW on selector. I’m going to have a look tomorrow and she asked me to pick up new programmer, is it likely to be this with power to the connections on programmer or could it be pump or MV. Sorry but I don’t do much fault finding and repairs although I’m industry, was just so I can pick a pump and MV up while at merchants, any advice welcomed, thanks !
 
Hi, thanks for all the advice, it was the pump that failed. Disconnected the pump from wiring centre and replaced 3amp fuse in spur, reset the trip and it was fine. Measured the ohms across the live/neutral and was 110 ohms, changed pump and got power at boiler cheers for the advice !
 