Hi,
I'm a first time poster with a skill set akin to that of a competent DIY'er I guess. I'm planning on replacing a old in efficient one pipe system with a flow and return. This will be done on our recently purchased bungalow which has an oil fired boiler. Whilst I'm confident a 22mm flow and return with 15mm T's for the 15 radiators will be sufficient in terms of heat carrying capacity, I'm concerned that the flow resistance posed by the long pipe runs will be excessive. I was therefore wondering if the entire flow and return down the centre of the house should be run in 28mm? The boiler is approximately 8m 50 from the spine of the house where a 14m flow and 14m return will run. Hopefully the plan below shows the layout in sufficient detail.
IMG_1630.jpg
I'd be grateful of any advice this forum could offer, thanks!
 
Plastic or copper piping ?
 
Have you calculated the heat loss / load of all the rads ?
 
Will be fine on 22mm but if you want to future proof a bit 28mm would be best and tee off in 22mm when there a run of 2 or more rads
 
Yes as at time of install cost is marginally more as it’s the same time to install
 
Hi,
Thanks, I was worried about the long runs of 14 from the boiler to the spine of the house then the flow and return circuit affecting the flow resistance across some 100m of pipe and 15 radiators. As I've no experience of putting in a system this large before I'd be really interested in why you think it's overkill? Thanks in advance.
OK I was abit lazy and just had a quick look.
Didn't soak in your 24kw heating requirement so yes 22mm is on the limit for MFR and with 100m of pipework your possibly at the higher end of head pressure for a standard pump.
It's fine I think (I haven't worked out your pressure losses) on 22mm but as said 28mm would perhaps be a better choice for main branches.
 
OK I was abit lazy and just had a quick look.
Didn't soak in your 24kw heating requirement so yes 22mm is on the limit for MFR and with 100m of pipework your possibly at the higher end of head pressure for a standard pump.
It's fine I think (I haven't worked out your pressure losses) on 22mm but as said 28mm would perhaps be a better choice for main branches.
Thanks very much knappers, appreciate you taking the time. A couple of last questions I had were:
1. Would taking the flow and return from the boiler to the main spine of the house in 28mm, then reducing the F&R to 22mm be a sensible compromise?
2. Is there any online calculator or guidance that I could use to work out the MFR?
3. I've now calculated each rooms heat requirements using an online calculator, rather than using the "whole house boiler sizing method". This suggests a heating requirement of 15kW for the CH and 2kW for the HW. Therefore it would seem wise to split the difference between the 2 results of 17kW and 24kW and call it a heat requirement of 21kW. Would this difference influence choosing 28mm over 22mm for the main branches?

Thanks again for help, really appreciated.
 
15/17kw seems like a much more normal requirement for number of rads. If your HW cylinder is next to the boiler then your heating pipework doesn't need to include the requirement for HW.
We're healthily back in the realms of 22mm pipe.

Flow rate(l/s) = kW/(4.2×temp differential)

Temp diff should be 20 or less (I'd use 15)
If you know your flowrates then you can workout pressure losses based on pipesize (or vice versa) for each branch and trunk, with a chart or calculator using velocity of between 0.75-1.5 m/s.
(Pressure Drop Online-Calculator - http://www.pressure-drop.com/Online-Calculator/)

Have fun!
 
Incase anyone is interested.
For UFH pipe sizing i'd use a temp differential of 10 or less
Thanks again Knappers. Once again I appreciate you taking the time. I guess I’ve been a bit spooked as currently the last 5 rads in the back half of the house do not heat up and apparently never have to any great degree. I believe this is most likely due to it being a one-pipe system though and hopefully not due to pipe sizing. The HW cylinder is 7m away from the boiler and plumbed in 28mm which I reckon could be a legacy thing from an old system. Whereas the CH is in 22mm. The current oil fired boiler is a Grant Vortex Utility 26-36 which again I reckon is over spec’d due to the old one pipe system. I intend to replace the boiler next year with a gas one by someone suitably qualified. Everything I’ve read suggests that replacing a one-pipe (albeit with a by-pass under each rad) with a two pipe will be worth my while in terms of efficiency. Does all of the above sound like sound logic or am I barking up the wrong tree? Thanks again
 
What do you mean when you say a bypass under each rad?
One-pipe systems can be temperamental especially if modified and modern hardware doesn't often work well with them.
You will have much more control over the system with 2pipes and you can use modern TRVs etc effectively.
 
What do you mean when you say a bypass under each rad?
One-pipe systems can be temperamental especially if modified and modern hardware doesn't often work well with them.
You will have much more control over the system with 2pipes and you can use modern TRVs etc effectively.
The feed for the rad is a 22mm it then reduces to a 15mm tail and a 15mm pipe that runs under the rad. This pipe then meets the other rad tail reducer and goes back up to 22mm …. on some rads. On others there is no bypass. Hope that makes sense?
 
I see you have never really gotten any cleverer with your answers

How far would you like me to go in-depth most of the time it’s lost on a diyer so tend not to confuse them
 
Well 22mm can carry 0.29lps which works out to around 24kw at dt20 with a 0.9mps flow rate

28mm will carry 0.49lps which works out to around 40kw at dt20 with a 0.9mps flow rate

Now with England recommending you start sizing your Emitters for a flow of 50dc eg dt20 rads eg ready for heat pumps your pipework needs to be sized the same

For example

22mm will carry 6kw with a dt 5 on water and 5.4 on gycol
28mm will carry 10kw with a dt 5 on water and 9.2 on gycol
 
Well 22mm can carry 0.29lps which works out to around 24kw at dt20 with a 0.9mps flow rate

28mm will carry 0.49lps which works out to around 40kw at dt20 with a 0.9mps flow rate

Now with England recommending you start sizing your Emitters for a flow of 50dc eg dt20 rads eg ready for heat pumps your pipework needs to be sized the same

For example

22mm will carry 6kw with a dt 5 on water and 5.4 on gycol
28mm will carry 10kw with a dt 5 on water and 9.2 on gycol
Keep going
 
Keep going

For that I would need pipework lengths / runs and emitter loadings which op doesn’t state and tbh not worth it on a free forum your more than welcome to spend your time on it though and send a full report to the op eg emitter sizing and pipe pressure losses/ pump head required etc 👍
 
How many boilers come with 28mm F&R these days and water is not compressable?

Same as why most heat only come with 15mm gas doesn’t mean I can run it straight from the meter in 15mm 20m etc (at 15kw)
 

Reply to Pipe sizing - Replacing a one pipe system with flow and return in the UK Plumbers Forums area at PlumbersForums.net