Paul Cochrane

New Member
Messages
9
Reaction score
0
Hi all!

Sorry if this has been asked before but i haven't been able to find anything out there...

We made our CH system zoned when I laid some UFH in the kitchen. (2 zones total: kitchen + rest of house) each zone has a Honeywell 2-port zone valve. The boiler is a Glowworm combi.

All is well with the system *except* when the heating isnt running and the system cools down. When this happens the pressure drops. HOWEVER if manually open one pf the honeywells the pressure instantly is fixed and returns to the normal 1.0 bar. For this reason I'mm 99% certain there isn't a leak in the system (pipes were all replaced 18 months ago)

I recently installed an auto-bypass valve thinking that this was the culprit. However, no matter what setting i change that to, the problem remains.

Any help greatly appreciated, if you need any further info do ask!

Cheers,
Paul
 

scott_d

Plumber
GSR
Messages
4,161
Reaction score
938
Any pictures?
Did you add an addition expansion vessel?
Is there a ufh manifold?
 
OP
P

Paul Cochrane

New Member
Messages
9
Reaction score
0
Hi Scott, thanks for your reply!

No I didn't add an expansion vessel, but yes there is a manifold for the UFH. Have added some pictures (it's still a work in progress as you can see! Sparky will sort cabling when he does 2nd fix)

Thanks,
Paul
 
OP
P

Paul Cochrane

New Member
Messages
9
Reaction score
0
Hi @scott_d here are the pics I mentioned earlier. the combi boiler is just above, out of shot, if you need any more info do just ask, thanks again!

Paul

IMG_20190219_092242.jpg

IMG_20190219_092354.jpg
 

scott_d

Plumber
GSR
Messages
4,161
Reaction score
938
Wow, what a mess!

How many rads and how big is the ufh?
What model of GW combi is it?
 
OP
P

Paul Cochrane

New Member
Messages
9
Reaction score
0
Yeah I know! I think a pro may be called in to put in some copper to neaten everything up, but in an effort to minimise exlense I've installed the UFH myself (also found it v difficult to actually get quotes for installation: no-one seemed to want to do it)

The UFH is a single run of 50metres. There are 7 rads in the house and the boiler is a Glowworm Easicom 24...

Thanks again,
Paul
 

Riley

S. Mod
Plumber
GSR
Messages
10,622
Reaction score
3,452
Which it might with no expansion vessel. I suspect no one wanted to fit it after you’ve begun. Nothing worse than picking up a job halfway through
 
OP
P

Paul Cochrane

New Member
Messages
9
Reaction score
0
Hi @scott_d @Riley just following up this thread again... So do you think the expansion vessel in the combi itself has died, or does the system now need a second EV because I've turned it into a zoned system? I'll have a look and see if there's any pressure in the internal expansion vessel if you think that's a good idea.

Will have time to fix that PRV today too!

Thanks
P
 

Harvest Fields

S. Mod
Plumber
GSR
Messages
9,552
Reaction score
2,168
Do not do that if the vessel is inside the boiler casing. You will need a gas safe registered engineer.
 

scott_d

Plumber
GSR
Messages
4,161
Reaction score
938
It’s probably undersized now you have increased the system size
 

Forum Sponsors

Corgi - Plumbing Supplies for Professional Plumbers - Plumb Advice

Plumbase - Plumbing Parts for Plumbers - Plumbers Advice

Power Shower Booster for Power Showers - Plumbing Advice

Underflor Heating Systems by uHeat - Plumbing Advice

Wetroom Supplies by Wetroom Store

Nicobond - Wetroom and Tiling Supplies - Plumbers Installation Advice

Corgi - Plumbing Supplies for Professional Plumbers - Advice for Plumbers

Do you have a DAB radio for work?

  • Yes

  • No


Results are only viewable after voting.

Latest Plumbing Advice

Top Bottom