Hi all,

Just curious - how often do you all replace the burner seal on a Worcester Greenstar during servicing?

Assuming all is well with combustion levels, pressure test, etc. (As without X-ray vision, one obviously can't see the state of it until you take it apart).

Thanks everyone,

Jennie
 

EvilDrPorkChop

Esteemed
Plumber
Gas Engineer
Messages
1,250
Worcester recommend they are done every 5 years. There was a technical bulletin about them, see attached.

I generally find it comes down to how much the boiler is used.
 

Attachments

    You don't have permission to view attachments. Attachments are hidden.

IND_Nick

Esteemed
Gas Engineer
Messages
323
I would second what Shaun said, every 4 years. If you leave it too long the whole service can be a nightmare with stuck baffles etc. It doesn't take long if the boiler isn't in an awful position to remove/clean/replace. I also replace the DHW restrictor at the same time as these are prone to failure. We'll maintained these boilers last forever, ish.
 

Jennie

Gas Engineer
Messages
280
Thanks everyone for the advice, and letting me know about the bulletin. I'll now be changing the gasket more regularly. :)
 

JusKel

Gas Engineer
Messages
36
Change them regularly. I came across this one that had failed to fire, but customer kept pressing the reset until it eventually fired. Luckily I got there before he burned the place down. Scorch marks on outside of casing and alot of heat damage to plastic parts.
 

Attachments

    You don't have permission to view attachments. Attachments are hidden.

moonlight

Plumber
Gas Engineer
Messages
948
Just done one the same just before Christmas. New wiring loom, electrodes, seal and electrodes leads. I think mine got off quite lucky. No scorching.
 

Gary.thornton

Messages
12
Always put your FGA around the electrodes to see if you get a CO Reading. Will often find the rectification electrode has gone down to a little nub too.
 

Reply to Worcester grecnstar burner seal (servicing) in the Gas Engineers Forum area at PlumbersForums.net

Similar threads

B
The only product I can find is: BWT AquaDial Combi-Care Compact 15 mm scale inhibitor (AC002100). I'm assuming this would be compatible with a...
Replies
3
Views
239
Bob Fleming
B
B
Check the copper pipe outside, if it’s leaking, then the noise could be the prv opening and closing.
Replies
3
Views
162
ChrisB1982
ChrisB1982
F
Thanks some good ideas. Just as an aside if we changed the existing boiler to a teamed/cascade setup with say two 30Kw domestic condensing boilers...
Replies
10
Views
419
FozzieBear
F
O
Replies
7
Views
2K
EvilDrPorkChop
EvilDrPorkChop
Creating content since 2001. Untold Media is a Registered Trademark.

Newest Threads (Please Reply)

Search Forum

Top