Hi everyone

Some very helpful people on this forum (hi John.g) sorted me out with some issues with a faulty installation of a Grundfos UPS3 back in Oct/Nov 2021.

My CH system has been running like a dream ever since. Until this evening.

For months we have been switching heat and/or water on/off manually as required due to energy bills. All good.

This evening we found that the heating was blazing away even though only the water was set to on on the controller.

Switched off both at controller but boiler kept burning and pump kept running.

Turned boiler setting down (from 3) until pilot went out.

Pump kept running upstairs. Left it 20 mins or so. Still on despite boiler now being fully switched off on front panel.

Turned off upstairs mains. Pump lost power and switched off.

Left for 5 minutes and switched mains power back on.

After 30 seconds pump switched back on (despite controller off) and simply will not switch off!

Any suggestions?

Boiler currently back on on front panel (set to 3). Water on/heat off on controller. Heating blazing!
 

Stephen JW

Messages
25
Stuck 2 port
Thanks Shaun

Totally novice here. You are referring to my Drayton MA1 right?
I get that if this is stuck that the water and heating would come on together regardless of whether controller is set to one or the other - but would that cause the Grunfos pump to keep running with both water & heat set to off?
Is it possible to reset the 2 port or are we talking about replacement?

Many thanks again!
 

ShaunCorbs

Staff member
S. Mod
Plumber
Gas Engineer
Messages
32,646
Solutions
3
Yes need to find with a multi meter where the live is coming from either 3 port or timer
 

Reply to Why won't my GRUNDFOS UPS3 pump stop running? in the Central Heating Forum area at PlumbersForums.net

Similar threads

S
Are there any indicator lights on on the pump when it's stopped?
Replies
3
Views
99
snowhead
snowhead
M
Clamp on thermostat on pipework near the offending pump. When the flow temp is less than ( say 50C ) the pump turns off. Not hard to install or...
Replies
3
Views
260
oz-plumber
O
Jonnyh88
Flow into rad in a One pipe is by gravity only, ie warm water rising up nearest vertical into rad. Any flow restriction has a great effect. So you...
Replies
6
Views
729
gpbeck
gpbeck
Fluke67
It doesn't have internal clock It doesn't have the internal clock and i have bypassed all that. Too easy I have actually been testing my spare...
Replies
2
Views
294
Fluke67
Fluke67
Creating content since 2001. Untold Media is a Registered Trademark.

Newest Threads (Please Reply)

Search Forum

Top