New to this forum but hoping you could give me a hand with some issues I'm having with my UFH.

I bought a house in Nov last year that has wet UFH in a kitchen extension. It's a relatively small area with only 2 loops, total 90m piping and 2-port manifold. Manifold model is Wunda Premium with it's own gate valve and pump.

The main issue with this is that the mixer valve 'sings' very loudly when it is allowing hot water from the boiler into the manifold - so much so that it wakes me up at night.
Second issue is that it causes the boiler to cycle in bursts of a few minutes at a time, and it overshoots it's set temp (the CH water temp) by quite a bit, before dropping back to a more reasonable number. The boiler pump stays running the entire time the UFH is on.

The boiler is a Baxi Duo-Tec 24kw. There are 2 loops from this, one to the 5 radiators in the house and one to the UFH, controlled independently by separate thermostats.
If the radiator loop is on at the same time as the UFH, there is no singing and the temp on the boiler is constant with no cycling.

Of note, there is no ABV between the flow and return to the boiler (although I gather there is one built into the boiler).

I have flushed and cleaned the whole system (radiator and UFH), replaced the mixer valve on the UFH twice and fiddled endlessly with the boiler CH temp with no success.

My thoughts are that there is not enough return flow to the boiler when just the UFH is on, probably due to the lack of a ABV, and the demand on the system is very low causing the boiler to cycle.
I think the singing is due to the pressure of the water through the mixer valve (particularly as it doesn't happen when the radiators are on) - again something which I *think* an ABV would cure.

Am I on the right lines here or totally off course? Any help much appreciated. Thanks!
 
We have found the only way to cure this is by doing the following.
1. Set the thermostat on the mixer to 47.
2. Turn the underfloor pump to the lowest setting.
3. Adjust the flow rates for each loop to achieve a 7 degree drop between the flow and return.
This normally cures it. But if it doesn’t fit an auto bypass valve just before the mixing valve.
Also properly range rate the boiler. This can help too
 
We have found the only way to cure this is by doing the following.
1. Set the thermostat on the mixer to 47.
2. Turn the underfloor pump to the lowest setting.
3. Adjust the flow rates for each loop to achieve a 7 degree drop between the flow and return.
This normally cures it. But if it doesn’t fit an auto bypass valve just before the mixing valve.
Also properly range rate the boiler. This can help too

Hi Chalked

Thanks for the thoughts. I have more or less done all these things - mixer is about 47 (which is what I need to get some heat through the wood floor), pump is on it's lowest setting and I've set the flow rates so they are pretty close to 7 degree drop over each loop.

I've also lowered the boiler CH temp to 50 in the hope that it stays lit and consistently provides 50 degree water...but it doesn't. The whistling and cycling continues.

Wunda have kindly sent me an Esbe valve to try to see if it stops the whistling - probably won't help the cycling boiler though.

At a bit of a loss really!o_O
 
I’ve had 6 wundafloor mixers whistling.
Even after they sent new ones it didn’t stop.
Found installing a bypass near the mixer cured it.
 
Hi Chalked

Thanks for the thoughts. I have more or less done all these things - mixer is about 47 (which is what I need to get some heat through the wood floor), pump is on it's lowest setting and I've set the flow rates so they are pretty close to 7 degree drop over each loop.

I've also lowered the boiler CH temp to 50 in the hope that it stays lit and consistently provides 50 degree water...but it doesn't. The whistling and cycling continues.

Wunda have kindly sent me an Esbe valve to try to see if it stops the whistling - probably won't help the cycling boiler though.

At a bit of a loss really!o_O

Just looking at this from the cycling point of view, if one assumed that your UFH is emitting 5 kw then based on your numbers above the boiler flow/return should be ~ 7 LPM & the UFH flowrate should be ~ 10 LPM with 3 LPM recirculating to give a mixing temp of 47C. If the UFH is only emitting 2.5 kw then boiler flowrate is 3.5 LPM, a UFH flowrate of 5 LPM & recirc of 1.5 LPM.
Based on the above you might consider just checking the cycling rate with the rads only in service and just keep shutting them down progressively until only one in service and see if the boiler actually modulates, when it reaches max turn down (to say 5 kw?) observe how long it runs for before cut out.
On UFH only the boiler might be reaching max temperature before it gets a chance to modulate but you probably have already looked at this. The above might tell you something.
As suggested above, range rating should help but IF its a combi boiler then is it possible to range rate the CH side & still have full output on HW??.
External ABV might stop whistling noise but I just don't know about the cycling as the boiler flow&return temps will be much closer depending on the amount of bypass.
 

Reply to Whistling UFH mixer valve & cycling boiler - no ABV? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

I have a plumber coming tomorrow to change a cartridge on a badly dripping tap on my bathroom mixer unit. There is no separate isolating valve for this tap so I'll have to close the stopcock. I tried closing it today but it won't go absolutely 100% closed and there is still a very slight flow...
Replies
1
Views
231
Our kitchen mixer tap has started dripping. Like so much of the plumbing in our almost new build bungalow, it is lacking! The plumber didn't install any isolating cocks in the H&C feed to the tap so how can I identify which of the valves is passing? Shut the whole H&C water system down?
Replies
12
Views
308
Hi All I have a leak coming from within my Mira Elite QT shower. It seems to be flowing from behind the switching Control. Any ideas what could be causing this leak. Already Changed the Pump Elbow as one of the clips had popped which was causing a second small leak, Any idea? Is it time to buy...
Replies
0
Views
223
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
300
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
229
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock