Discuss water help no hot water in the Central Heating Forum area at PlumbersForums.net

OP
J

jpbroad1970

Member
Messages
79
Reaction score
20
Progress update, plumbers have been today, 3.5 hours and looks like we are functional. It looks like it was air. They have simplified the pipework in the airing cupboard. Still sounds like a bit of air in the pipework though. Pump is running between 31 and 33w.
 

John.g

Active Member
Messages
351
Reaction score
40
Progress update, plumbers have been today, 3.5 hours and looks like we are functional. It looks like it was air. They have simplified the pipework in the airing cupboard. Still sounds like a bit of air in the pipework though. Pump is running between 31 and 33w.
That's great news JP, that airing cupboard is well named. You should be circulating ~ 10/12 LPM if on speed 3. (6M)
 
OP
J

jpbroad1970

Member
Messages
79
Reaction score
20
Well unfortunately the saga continues, everything worked great Friday Saturday Sunday Monday then as we got up this morning FD error back on boiler. Give them their due plumbers back out today but couldn't get it going. They are thinking heat exchanger but won't commit till boiler stripped as as you all know they are expensive.:eek:
 

John.g

Active Member
Messages
351
Reaction score
40
Sorry to hear that but I suppose really not that surprising as a 6M head was required to circulate ~ 10 LPM.
 

Ziggie

New Member
Messages
13
Reaction score
2
Restating testing mentioned earlier.
Switch demand for heating and hot water off on programmer and turn down both thermostats.
Now switch off power to the entire system using the spur box.
The 3 port should move to hot water setting.
Now select hot water on programmer and turn cyl thermostat up.
The 3 port should remain at hot water setting and boiler and pump should start.
Now switch hot water off on programmer and turn down cyl thermostat. Boiler and pump should stop , the pump may run on for a few minutes after the boiler stops.
Now turn on demand for heating and turn the room thermostat up.

The 3 port should move to heating and the boiler and pump should start.

Now, request hot water and turn up the cylinder thermostat.
The 3 port should move to the middle position.

Post the results of the 3 tests here which would help diagnostics.
Post automatically merged:

Obviously, switch on the mains to do the testing - missed the step oops
Post automatically merged:

Sorry just got the previous update - after I posted.

Just ignore
 
OP
J

jpbroad1970

Member
Messages
79
Reaction score
20
Righty ho this is the latest, blocked heat exchanger, plumbers today have managed to unblock part of it but it's buggered really, short term fix very short term so we are having a new boiler fitted next week or week after as it will give us 10 year warranty. Could just just change heat exchanger but we will feel better with new boiler.
 

CBW1982

Plumber
GSR
Messages
1,125
Reaction score
215
Righty ho this is the latest, blocked heat exchanger, plumbers today have managed to unblock part of it but it's buggered really, short term fix very short term so we are having a new boiler fitted next week or week after as it will give us 10 year warranty. Could just just change heat exchanger but we will feel better with new boiler.
Glad you finally got to the bottom of it
 