Hi,
I need to connect 2 X 2 port valves to my boiler via a 10 way junction box.
My boiler needs a zero volt switch line so I think I need to install a relay, in series, between terminal 9, coming from the valves, to the boiler.
Any ideas what I need or when to get 1?
Cheers,

Keith.
 
Messages
964
1. I'm assuming you mean that in order to fire the boiler, you need a switch with no voltage on it to connect the two relevant boiler terminals.
2. Two way valves (normally) have five wires:
2a. Blue, which is neutral.
2b. Green / yellow which is earth.
2c. Brown, which is live to the motor valve.
2d. Grey, which is one side of a microswitch.
2e. Orange, which is the other side of the switch.
3. In a traditional voltage switching system:
3a. The programmer outputs 230V during an "on" cycle. This output is connected to the thermostat.
3b. If the thermostat sees heat is needed, It switches 230 v onto its output, which is connected to the motor brown wire.
3c. The motor's grey wire is connected to mains 230V, usually in the wiring centre. Because the microswitch in the valve is normally open, that 230V doesn't go anywhere.
3d. When the motor opens the valve, as it reaches the open position, it closes a microswitch and sends 230 V to the boiler from the grey wire via the orange wire.
3e. The boiler fires.
4. Because the grey and orange wires are either side of a switch, unless connected to anything else, they are a zero voltage item.
5. If you connect the grey and orange wires across your boiler terminals, they will constitute the required switch without the need for a relay.
6. I'd suggest testing it first. Providing you have the expertise and equipment:
6a. Make sure the earth is connected at all times.
6b. Power the motor brown and blue from the mains.
6c. Use a multi-meter to check for the absence of voltage across grey and orange.
6d. Do a continuity test across the grey and orange provided there is no voltage present on them.
 
Messages
10
1. I'm assuming you mean that in order to fire the boiler, you need a switch with no voltage on it to connect the two relevant boiler terminals.
2. Two way valves (normally) have five wires:
2a. Blue, which is neutral.
2b. Green / yellow which is earth.
2c. Brown, which is live to the motor valve.
2d. Grey, which is one side of a microswitch.
2e. Orange, which is the other side of the switch.
3. In a traditional voltage switching system:
3a. The programmer outputs 230V during an "on" cycle. This output is connected to the thermostat.
3b. If the thermostat sees heat is needed, It switches 230 v onto its output, which is connected to the motor brown wire.
3c. The motor's grey wire is connected to mains 230V, usually in the wiring centre. Because the microswitch in the valve is normally open, that 230V doesn't go anywhere.
3d. When the motor opens the valve, as it reaches the open position, it closes a microswitch and sends 230 V to the boiler from the grey wire via the orange wire.
3e. The boiler fires.
4. Because the grey and orange wires are either side of a switch, unless connected to anything else, they are a zero voltage item.
5. If you connect the grey and orange wires across your boiler terminals, they will constitute the required switch without the need for a relay.
6. I'd suggest testing it first. Providing you have the expertise and equipment:
6a. Make sure the earth is connected at all times.
6b. Power the motor brown and blue from the mains.
6c. Use a multi-meter to check for the absence of voltage across grey and orange.
6d. Do a continuity test across the grey and orange provided there is no voltage present on them.
Thanks,

I was looking at this type of set up.....
You don't have permission to view attachments. Attachments are hidden.

But maybe this'd be better.

You don't have permission to view attachments. Attachments are hidden.
 

Attachments

    You don't have permission to view attachments. Attachments are hidden.

Reply to Volt Free Relay in the Central Heating Forum area at PlumbersForums.net

Similar threads

D
It appears my heating system is throwing a wobbly; I have a system boiler set-up (Ideal Standard ... I think, can check), hot water works fine but the heating is problematic. When I adjusting the thermostat (Drayton RTS8, running on 24vdc) to kick the heating in to life results in relay chatter...
Replies
2
Views
511
DocMonkey
D
K
Hi, Looking for some advice please. I live in france. We have a house with an attached cottage. We have no heating in our house but the cottage has a combi boiler and central heating rads. Seeing as this cottage is rarely used in the winter it seems daft not to add some rads to the boiler for...
Replies
2
Views
121
ShaunCorbs
ShaunCorbs
O
Hi all, first of all I'm not a plumber so forgive my ignorance. We are currently getting a boiler stove installed. This involves connecting the plumbing and some electrical to our existing heating system. The Plumber has requested that our electrician installs a spur at the location of the...
Replies
2
Views
3
olestoepoke
O
W
Boiler is a Viessmann 100-w (2021 version) heatmiser uh8-rf heatmiser rf switch (intended for boiler enable only) Heatmiser neoair thermostats I live so far north that there isn't a Viessmann installer local to me, however after speaking to Viessmann my local heating engineer was placed on a...
Replies
10
Views
161
Timmy D
T
M
Hello, I've previously had an issue with my boiler pressure getting too high with the central heating on and needing a reset. I had a gas plumber come round and he swapped the expansion vessel. The pressure issue seems to be fixed but now there is another issue... When I turn the central...
Replies
6
Views
195
ShaunCorbs
ShaunCorbs

Newest Threads (Please Reply)

Search Forum

Top