Just had a new Viessmann Vitoden 100w heat only boiler installed, I have to turn the dial all the way to max just to get some decent heat, if I turn it all the way (so it's pointing at reset) it'll settle at around 76 degrees. Is this normal? It's modulating fine, I was maybe expecting to set the dial at the dot at 4, but that's not hot enough to heat the hot water cylinder. Pump is on medium speed setting, any slower and some of the rads don't heat up.
IMG_20181215_110622.jpg
 
I would say it's modulating down due to the temp rise
 
Just turned my one up to max & got high 60's so I would guess you have Weather comp on, If you boost the hot water does the rad disappear to be replaced with a tap?

I don't think I have weather comp, no mention of it by the installer. I don't have a hot water boost, it's a traditional heat only boiler. Cylinder stat is set to 65.
 
does the temp go up to about 65 degrees then drops down then back up then down if so its a flow problem the return temp is out of alignment with the flow (too great a difference)
 
does the temp go up to about 65 degrees then drops down then back up then down if so its a flow problem the return temp is out of alignment with the flow (too great a difference)
No once it's got up to temp and modulated the flame height down, the temp stays constant, have it running at 72 at the moment and seems fine although still not sure the rads are as hot as they were on my old Baxi.

Something else I noticed, I've had a F2 fault code (temp limit) and noticed after the boiler shut down that the latent temp kept going up and up and up, seems I don't have pump overrun any more which I had on my old boiler. Something else to call the installer about tomorrow!
 
Here's the heating curves, doesn't say what they are without WC though. But position 6 should generate temps between 60-90, hence wondering why I can't get more heat when dial is on max...

heat curves.JPG
 
thats the curve for wather compensation what controls do you have. is there a small white box on the outside of your house on a north or north west wall may be high up
 
I doubt if this has WC , its not required for boiler plus , its just combis unless somebody knows different .
IMO the boiler is working fine , if the rads aren’t as warm as your old Baxi , it will be because it probably wasn't a condensing boiler and had a much highter flow temp .
 
The best advice is to get your installer back , post a picture of the install is the benchmark section completed in the installation manual it would be interesting to see the figures? how long did the install take . Kop
 
Install took about 4 hours in total, no idea if that's quick, it felt quick to me. I've kept the same controls. There's deffo no WC on this and thinking about it more I don't think it would work as in summer there wouldn't be enough heat for the DHW.

Anyway here's some more pics...

Before:
IMG_20181123_102737.jpg


IMG_20181202_124532.jpg

During:
IMG_20181214_090917.jpg

After:
IMG_20181216_171705.jpg


Benchmark (interesting return temp there, but I am going to go round all the rads anyway and rebalance them for a 20 degree drop if I can):
IMG_20181216_172702-edited.jpg
 
Oh dear thats not right I am afraid to say that you have a poor install there bud have you paid this chap? please say no Is he a approved installer for viessman I very much doubt it looking at that, get gas safe out to inspect the job 4 hours for a install has alarm bells ringing it takes longer than that to do a chemical clean the gas supply will most probably be undersized do you have other gas appliances this could be a serious problem . All the best Kop
 
22mm gas pipe runs to behind the kitchen unit (where there used to be a floor standing boiler) then reduces down to 15mm for the last 1.5m, so I believe the gas supply is okay although don't know if the gas rate in the benchmark indicates an issue. There are no other gas appliances in the house.

Not sure how thoroughly the system was cleaned, he said the water in my system was already clear, no discolouration, probably because I flushed it and added inhibitor in the summer. The paperwork says he used MC1, no idea what that is.

This was all done through Hassle Free Boilers, they are accredited by Viessmann, I checked before buying as wanted the 10 year warranty. I'll be calling tomorrow to make sure they register it.
 
22mm gas pipe runs to behind the kitchen unit (where there used to be a floor standing boiler) then reduces down to 15mm for the last 1.5m, so I believe the gas supply is okay although don't know if the gas rate in the benchmark indicates an issue. There are no other gas appliances in the house.

Not sure how thoroughly the system was cleaned, he said the water in my system was already clear, no discolouration, probably because I flushed it and added inhibitor in the summer. The paperwork says he used MC1, no idea what that is.

This was all done through Hassle Free Boilers, they are accredited by Viessmann, I checked before buying as wanted the 10 year warranty. I'll be calling tomorrow to make sure they register it.

They might be but the company that installed it isn't

So no 10 year warranty
 
Mc3 is a cleaner which needs to be circulated through your system for a minimum of 2 hours , mc1 is the inhibitor added when fully commissioned and tested , again your choice but I would have the install inspected by gas safe it costs you nothing and you will have peace of mind your safe and your boiler warranty will be intact . Kop
 
First of all I would contact Viessmann and check what warranty you have serial no is ontop of the boiler right hand side of the flue

Also you would on a system have a flow temp of 65-70 dc and a return temp of 50-55dc
 
where did you see the 10 years warranty offered by them just had a quick look cant find anything on there site?
 
It's in their quote:

Hassle Free Boilers
1 Viessmann Vitodens 100W 26kW Heat Only Boiler
Including:
- Boiler supply and installation
- 5 year Viessmann manufacturer warranty
- 2 year workmanship warranty
- Magnaclean magnetic filter
- Supply and installation of boiler flue and controls
- Full system clean, flush and protection*
1 Viessmann Warranty Extension (Additional 5 Years)
1 Condensate Soakaway
1 Viessmann Horizontal Flue Kit
1 Heat Only/System Boiler Installation Pack (22mm)
 
:D love the *

"Full system clean, flush and protection*"

in short 5 years as standard

then the warranty extension eg you paid to have it upgraded

Condensate Soakaway ?????? should be a white pipe below the boiler where does that go (breakfasts in the way to see)

also looks like the flue is running downwards to the outside should be the other way so theres a fall to the boiler
 
Here's the asterisk:

* The system clean and flush involves the system being flushed with mains pressure water and appropriate cleaning chemicals. We will not complete a 'powerflush'. A 'Magnacleanse' clean is an alternative to a 'powerflush' and is available as a chargeable option where advised or requested.
 
Reason I'm querying the pump overrun is I had an F2 fault code (temperature limit) think it was due to the latent temp rising in the hex after shutdown and triggering a fault - it's been okay since I turned the flow temp down a bit but wondering if this happens a lot when there's no pump overrun.
 
Reason I'm querying the pump overrun is I had an F2 fault code (temperature limit) think it was due to the latent temp rising in the hex after shutdown and triggering a fault - it's been okay since I turned the flow temp down a bit but wondering if this happens a lot when there's no pump overrun.

Nope dont need pump overun , could have been air , they do airlock on installation, once its gone they arent a problem.
 
Looks like a typical “thrown - in” boiler rather that a fitted one . 4 hours , Lol .

Well, I kinda feel like I agree with you, I was surprised when they said they had finished, it all just felt a bit rushed.

I did try and find a local installer but half the time the phone just rang and rang, or I left a message and no-one called back, or they didn't do Viessmann, or they couldn't offer any interest free credit... in the end I was kinda exasperated and just went with HFB because they were cheap, could do Viessmann and did 3 years interest free credit. I already had a nagging feeling after talking to them that they would just sub it out (despite asking if they used their own people). I couldn't see how they could offer national coverage without using subbies. And the two guys that turned up had come all the way from Rotherham (I am in Hampshire).

Anyway, my main priority is to ensure I get the 10 year warranty so will be asking them for proof of this tomorrow (and I'll double check with Viessmann too). If no proof is forthcoming then they'll be in breach of contract as that's what I paid for,
 

Reply to Viessmann boiler set at max just to get enough heat in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

D
hello! while saving up for a new plumbing and heating installation for my new one bedroom flat, i did a lot of research on different boilers and systems, sought some advice, and settled on a viessmann vitodens 050-w, seems to offer a lot in terms of features and reliability, offers good value...
Replies
51
Views
4K
So a strange conundrum regarding water temp if anyone can help resolve, would be much appreciated. Ive tried to give as much info as possible to give a full picture but let me know if ive missed anything. I have a Baxi Avanta 25h heat only boiler. Works fine. Unvented 300ltr megaflow. Stated...
Replies
1
Views
145
Hi, I have a Vailant EcoTec Boiler with a Megaflo. These are controlled by a Honeywell controller. I have one 3 port diverter, where one of the outputs goes to a 2 port diverter prior to the Megaflo (I believe this is some safety feature). I have run into an intermittent problem where some...
Replies
5
Views
221
M
Hello, We’ve recently moved into a fairly old, fairly big detached house (i.e. fairly draughty, but not too bad by any means) with a fairly new well maintained Worcester combi boiler. We weren’t convinced the heating was working right and then got hit with a £610 energy bill for the first 6...
Replies
0
Views
247
MartinPod81
M
We are a few months into our Viessmann Vitodens 100-W 19KW Heat Only boiler and it is working fine. We replaced an old 1999 Baxi. Our house is a 2 bathroom 4 bed detatched, built 1999. The engineer did not really know the Viessmann boiler and I am not convinced his approach of “turn everything...