Paul Mc

Gas Engineer
Messages
6
Hi All

Has anyone ever questioned the reasons why Vaillant MIs for their vertical flue termination refer to damp exhaust air escapes from “channel vents” may condense in the air pipe and cause damage to the product, this would suggest that the flue terminal has to be at least 1 meter away on either side from a soil pipe and at least 3 meters above if the soil pipe is below

the attached photo is taken from the MI on page 4

I appreciate the obvious answer is to phone Vaillant Technical, however it being a bank holiday and a flue termination position diagram that I had not seen before I thought it might be useful to ask the forum

Thanks

Paul
 
Last edited:
Hi Scott

That makes sense, however you would guess that would only have a temporary affect on combustion depending on the weather conditions and wind directions, however the MI state it will damage the product, so this makes me think the damp air will damage the air intake flue?
 
I don’t know the science but I assume if you draw in lots of methane and mix it with gas it could create an explosive mixture.
It could also be corrosive to the metal outer flue it damage the rubber flue seals.
 
Hi Scott, a boiler flue only needs to be a minimum 300mm away from a cooker extractor vent which is definitely pushing out contaminated air, I agree you will have contaminated air which contains moisture leaving a soil stack and had the MI stated 300mm may not have given it further consideration however the diagram states 1 meter and 3 meter, Ive tried to attach the photo from the MI however it keeps getting blocked

Thanks

Paul
 
This one,, (won't post as an image, tech issue at the moment I beleive)

I assume they mean air from a Soil and vent pipe or Shower / Bathroom extract condensing in the boiler air inlet tube and the water running into the casing.
This wouldn't happen in a horizonatal flue.
(needs minimum 20 characters per post, still)

View attachment Vaillant flue roof.PNG
 
Last edited:
This one,, (won't post as an image, tech isue at the moment I beleive)(needs minimum 20 characters per post, still)

View attachment 43684
This one,, (won't post as an image, tech issue at the moment I beleive)

I assume they mean air from a Soil and vent pipe or Shower / Bathroom extract condensing in the boiler air inlet tube and the water running into the casing.
This wouldn't happen in a horizonatal flue.
(needs minimum 20 characters per post, still)

View attachment 43684
Hi
This one,, (won't post as an image, tech issue at the moment I beleive)

I assume they mean air from a Soil and vent pipe or Shower / Bathroom extract condensing in the boiler air inlet tube and the water running into the casing.
This wouldn't happen in a horizonatal flue.
(needs minimum 20 characters per post, still)

View attachment 43684
This one,, (won't post as an image, tech issue at the moment I beleive)

I assume they mean air from a Soil and vent pipe or Shower / Bathroom extract condensing in the boiler air inlet tube and the water running into the casing.
This wouldn't happen in a horizonatal flue.
(needs minimum 20 characters per post, still)

View attachment 43684

Hi Snowhead

Yes this is the flue termination position diagram that I tried to post, still interesting that Vaillant believe that damp air from a soil pipe or extractor, which I would guess would be warm and rising, could find it way into an adjacent vertical flue if the flue is closer than 1 meter either side or less than 3 meters above, Ive not seen this diagram with any other MIs

Thanks

Paul
 
Has anyone ever questioned the reasons why Vaillant MIs for their vertical flue termination refer to damp exhaust air escapes from “channel vents” may condense in the air pipe and cause damage to the product,
My guess is that the instructions were originally in German and used the word 'Kanal', which can be translated to English as 'channel' but also means 'sewer' or 'duct', etc. Evidently the translator picked the wrong one for this context.
 

Reply to Vaillant Ecotec vertical flue minimum distance from soil pipe in the Gas Engineers Forum area at PlumbersForums.net

Similar plumbing topics

Morning all, as always can never find an exact existing thread / discussion where I don't feel like I'm making one too many assumptions. Can I get a quick sense check on the below, always wanting to work 1 step ahead, eventually planning to add an en-suite to my existing loft conversion. Got...
Replies
3
Views
1K
Hi, I have just noticed a damp patch around where my boiler flue exits through to outside wall along with a rusty colour around the collar of the flue bend. I’ve checked the external wall & there’s no water coming in from outside but the flue terminal also has a rusty colour. My regular boiler...
Replies
4
Views
1K
Not long bought a house with a second story loft conversion to dorma which contains an en-suite. Toilet in en-suite has a flex waste pipe from spigot directly to top of the vertical soil pipe with not much clearance. Soil stack has no ventilation on 2nd floor causing drain smell in the en-suite...
Replies
2
Views
988
Deleted member 120897
D
Hi all, came across this forum this looking for information on my sooting up kitchen type indoor Enviromax. I'm a retired electronics/maintenance engineer, (fwiw can answer questions on popular smart home thermostat systems), but I've installed many solid fuel boilers in the last 40 years for...
Replies
5
Views
2K
Hi, Need some advice about a soil pipe in 1966ish built ex-mod property. We have suspected but not be able to prove that since some heavy vibration from Pilling for a school across the road was done that our soil pipe has cracked, we are 99% sure it's cast iron from what neighbours have said...
Replies
5
Views
16K
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock